Good info. He did state the there was a restriction somewhere in the system. He OHM'd the motor/ windings in the motor and got a 1000 or something like that. Electrically, the motor checks out, he says.
Also, the fan just started making a humming noise when running with no A/C and pushing just ambient air. Could that be the source of the problem?
-
10-05-2012, 11:43 AM #30
Regular Guest
- Join Date
- Oct 2012
- Posts
- 21
-
10-05-2012, 11:46 AM #31
Regular Guest
- Join Date
- Oct 2012
- Posts
- 21
I am starting to get the feeling that I am being fooled. I asked again about the metering device and he said that he could not tell what my system had without opening up the evaporator case and that he "assumed" the system was a TXV system because of the way it was behaving.
I don't like pay professionals for assumptions, I need results...
-
10-05-2012, 11:52 AM #32
Regular Guest
- Join Date
- Oct 2012
- Posts
- 21
I asked about the metering device and he stated he would have to open up the evaporator coil to find out the metering device my system has. He said that sometimes the condenser will say if the system is a TXV system, cap tube or whatever device the system has.
I asked him to clean out the metering device, based on your post earlier in this thread. He said that he has never had someone ask him to do that before and that it would only be a 50/50 shot at working. He said that is there was any sediment in the line that it would have been cleaned out when he did the evac, purge and refill. What do you think?
-
10-05-2012, 11:56 AM #33
Regular Guest
- Join Date
- Oct 2012
- Posts
- 21
I asked again about the capacitor and he said that it was bad becuase it was rated at 5% and it was reading at 4.7%.. He changed it because it needed to be changed anyways...
I am not getting a good vibe from contractor #3, especially after he changed the capacitor and it really didn't fix anything. I am hesitant to get ANOTHER contractor because that is too many people working on my A/C. I am getting the feeling that they are taking advantage of their position and scamming their customers.
-
10-05-2012, 11:58 AM #34
Regular Guest
- Join Date
- Oct 2012
- Posts
- 21
On my telephone conversation with him today, he said that he didn't like what was going on with my system because he can't figure it out and it make him look bad. I told him that his credibility took a hit when he changed out the capacitor and it didn't fix anything. Seems like he is just taking shots in the dark, as its been said in this thread.
-
10-05-2012, 12:02 PM #35
Hey a 50 50 shot is better than what you have been getting. Seriously You have got to find someone that can figure out whats going on. Now your fan motor is not operating correctly. I just don't get it. Humming fan motor???? You mean they haven't checked the operation of the fan motor with a symptom of freezing coils??? Also it is possible to determine metering device by checking pressures and tempuratures at condenser.
-
10-05-2012, 12:58 PM #36
Well, I said Contractor #3 showed promise, but that may be dimming a bit.

A seasoned tech can often tell what type of metering device is on a system without actually going to look for it. In the olden days, if a TXV was on the system, the single phase compressor had a start-assist kit on it. Nowadays, with scrolls, not always the case. However, when measuring a system, if it has a TXV on it, the superheat will remain pretty steady as the heat load on the evaporator changes and the condenser head pressure changes, whereas with a piston, the superheat will change with evaporator load and condenser head pressure. If a TXV fails, it often fails closed, as the only opening pressure on a TXV is the bulb pressure. A failed TXV will typically starve the evaporator of refrigerant, resulting in very high superheat, low suction pressure, and low head pressure.
Of course, whether a system has a TXV or a piston metering device on it, if there is trash/debris in either device, it can act like what Contractor #3 described, where everything seemed fine and suddenly it was like someone closed down on a valve. A metering device of whichever type is the smallest passage in the system, so any trash that freely circulates in the system WILL get hung up here, if it is large enough.
Contractor #3 needs to educate himself on what an evacuation, purge, and refill does to a system. Will it remove solid debris? On the purge phase, maybe some. Even then, only if he's doing a purge a certain way. But that is not how things are done right. To catch debris, you install a liquid line drier ANY TIME THE SYSTEM HAS BEEN OPEN TO THE ATMOSPHERE. And you flow nitrogen while brazing in that new liquid line drier, and for any other work done on the circuit that requires brazing. The liquid line drier serves two functions; it filters the system, and it catches any remaining moisture that could not be removed by a vacuum pump.
Evacuating a system does not remove solid debris. Evacuation is for removing moisture and air (non-condensibles). Purging is mainly done with nitrogen and a product to rid the system of oil...either because oil is logged up somewhere in the system, or the tech is converting the system from mineral oil to POE oil. Purging is NOT done to get moisture and air out of the system, and it won't remove all of the solid contaminants."In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
10-05-2012, 02:41 PM #37
Regular Guest
- Join Date
- Oct 2012
- Posts
- 21
I think that I am going to go with a 4th contractor. He has been in the industry for 18 years and comes recommended from a property manager friend that has lived in the area for over 40 years. He will be at the property tomorrow, so Ill post what he finds out.
Thanks for all the inputs thus far. You guys are really great!
-
10-05-2012, 02:49 PM #38
Regular Guest
- Join Date
- Oct 2012
- Posts
- 21
How would debris get into the system to begin with?
-