    Don't see this much
    Oil fired wtr heater. Name:  ImageUploadedByTapatalk1349219457.801671.jpg
    Jul 2009
    Columbia, MD
    why do oil furnaces always get freakin barometric dampers but, everyone is so dang scared to install a barometric on a gas appliance.
    geeeeeezzz!!
    May 2012
    Upper Michigan
    Quote Originally Posted by gravity View Post
    geeeeeezzz!!
    Not sure, we never install 80% up here so never thought of it lol.
    Aug 2012
    NE wisconsin
    geeeeeezzz!!
    Because the gap between the water heater and the vent pipe serves that purpose and it doesn't need one.
    Apr 2011
    Coastal Maine
    I wouldn't put this in the wall of shame. Other than the unsleeved oil line, these old Aero's worked fine. Bock's were the same. They can make more hot water than a family can use.
    May 2012
    Upper Michigan
    Quote Originally Posted by meplumber View Post
    Oil is very expensive is all
    May 2012
    Upper Michigan
    Quote Originally Posted by philjafo View Post
    I was thinking furnace for some dumb reason
    In a machine room
    A draft hood (or gap as you put it) serves a completely different purpose than a barometric. According to ASHRAE a draft hood isolates the appliance from the flue allowing combustion to take place without venting action. Since it disconnects the appliance, draft and air through the burner is completely uncontrolled. Draft hoods are designed for a specific set of conditions, which are; a vent of not more than 5 ft in height with 1 or 2 elbows. How often do those conditions get met in the field???
    A barometric or draft regulator on the other hand allows for a consistent amount of air through the burner that does not change with changing conditions. Those of us who test for CO find draft hoods spilling quite often, either with higher than normal or lower than normal flue draft pressure. They are not safe under all conditions! A draft regulator is the only way to fix them. A spill switch added to the bottom of a double swing barometric will shut down the burner if the flue gets blocked.
    In a machine room
    geeeeeezzz!!
    May 2012
    Upper Michigan
    Quote Originally Posted by Joehvac25 View Post
    Wth guess he did say furnace.
    In a machine room
    I work on quite a few oil burners but have only seen 2 oil fired water heaters. Most of them got changed to electric it seems.
    Oct 2012
    Torrington CT
    up here in CT i have worked on so many to oil fired water heaters the pain in the butt part is to clean them when there is no room for your brush
    Mar 2012
    New Hampshire
    I cleaned 2 today, we have tons of em' up here in Patriots country!