10-02-2012, 01:59 PM #1
At what outdoor dew point is a dehumidifier not needed in a basement?
I have been waiting all summer to answer this question. This is 1,700 sqft. finished basement that I monitor. There are two occupants in the home 12 hours per day. No fresh air ventilation or dehumidification this week. The basement was <53%RH for the week. The outdoor dew point average <40^F for the week. This is a cool basement without much space heating yet. At higher outdoor dew points, I needed dehumidification.
I posted the data from my Hobo loggers.
Regards TB
WI 50RH Bsmnt No dehu.pdfBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
10-02-2012, 03:04 PM #2
so coooool! (I just got 4 Ecobee's - put 2 in my rental - there is so much to learn from knowing how stuff actually performs.)
I see you are targeting a 5f air temp delta but maintaining 15-20f. How did you arrive at those decisions?
How do you guesstimate the temperature of the coldest surface?Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.
-
10-03-2012, 01:27 PM #3
I delayed turning the heat on till this week. The smell of the basement is a good indication of excess dew point. Usually 50%RH in the basement is enough for carpet on the concrete.
I am attaching a illistration of the balancing effect of air moving through the home with a given amount of moisture load.
Changing any of the inputs will change the %RH in the home. Controlling the %RH requires adding or removing moisture from the air in the home. Dehumidifier or humififier!
Regards TB
Microsoft Word - Moisture balance in the house.pdf
WI 50RH Bsmnt No dehu.pdfBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
10-03-2012, 02:12 PM #4
Regular Guest
- Join Date
- Sep 2002
- Location
- I don't know
- Posts
- 2,888
Interesting data - thanks.
The type of moisture protection around the exterior side of foundation, as well has precipitation has a huge impact from my experience.
A basement can still be damp even when the outdoor dewpoint is well below 50F due to moist soil and/or precipitation.
With no damp/waterproofing - typical of older foundations, it might be necessary to occasionally run a dehumidifier or ventilate when it rains well until december or so.
-----------
One thing I'm curious about is how much latent heat consumer grade dehumidifiers convert to sensible heat relative to total energy consumption.
Say a 50 pint unit consumes 500 watts when the compressor is running - about 1700 BTUs/hr.
How many extra BTUs/hr would be released at 75F/50% humidity?
What's the effective cop when it comes to heat production? Example: 0.2 units of latent heat converted into sensible heat would be 1.2
-
10-24-2012, 11:28 AM #5
End of Oct in WI shows low dew points and then switch to +60^F. Interest effect on a ERV home with .4 ach CO2 control. This a foamed walls home.
The inside %RH tracks the outdoor dew point to the point where the dehu is activated.
Regards TB
Data by Hobo Loggers
10 23 12 erv home 2-789823-16-160.pdfBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
10-25-2012, 01:18 AM #6
I've started an album of chart screenshots from my Ecobee portal. Look what can be learned by tracking how a home and it's equipment interact with each other and the environment.
This thing tracks indoor, outdoor temps, run time, and RH.
Each vertical red line represents up to 5 minutes of run time.
Green line is indoor temp
Black is outdoor temp.
Dotted red is set temp
Grey/light blue is RH
Really interesting to see cycle time and impact. TB - interested in your thoughts about rh line.
Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.
-
10-25-2012, 06:51 AM #7
I could not blow up the picture enough to see the detail. Any chance you could post a PDF of the graph.
WI has +60^F outdoor dew point this week, it headed your way.
I have data on effect on a basement without dehumidifier. The house is getting about 40-70 natural infiltration this week. Basement zooming up.
You can see the outdoor dew point drive the indoor dew point/%RH. Aggresive air change would cause higher indoor %RH. OK for a day or two. The lag is the material of the house absorbing moisture. Mechanical ventilation and a good dehu is one of the near perfect solutions. This WI's high dew points last gasp.
Attaching PDF of data.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
10-28-2012, 11:05 AM #8
Professional Member
- Join Date
- Aug 2006
- Posts
- 2,439
It's not the Outdoor Dew Point you need to worry about. It's the Indoor Dew Point, you need to find your coldest indoor basement surface Temperature. It could be a window pane or frame. Masonry wall or floor. It could also switch places over the seasons. I.E. Floor in Summer, Window in Winter. My Basement is much dryer since I put deeper sump pits in. Went from 24" to 36" Also put a Watch Dog system in so I don't flood during storm power outages.
-
10-28-2012, 12:52 PM #9
So even pics at google + are too low? Hmmm, good to know.
I can get XML. Please send me your email.Which makes more sense to you?
CONSERVATION - turning your thermostat back and being uncomfortable. Maybe saving 5-10%
ENERGY EFFICIENCY - leaving your thermostat where everyone is comfortable. Saving 30-70%
DO THE NUMBERS! Step on a HOMESCALE.
What is comfort? Well, it AIN'T just TEMPERATURE!
Energy Obese? An audit is the next step - go to BPI.org, or RESNET, and find an auditor near you.


Reply With Quote