    Quote Originally Posted by rustneversleeps View Post
    thanks kls-ccc my next post will have all the info.i needed to be taught how to ask question on here i think i got it now, thanks again
    My post has nothing to do with how you ask the question, but questions you should be asking yourself before you asking anyone else.

    It is all part of the proccess of diagnostics. 1st step is what is the sequence of operation? #2 where does that sequence stop?, why?

    Yes, diagnostics can be more detailed than that, but often times it's that simple. Intermitant problem can be hard to reproduce but it still follows the same proccess. If you understand the sequence of operation and how each step properly operates, when you take all the measurements you will see what the problem is, without having to bring anyone else in.

  2. #22
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Another question; When the compressor starts running do you have to chase it down?

  3. #23
    Join Date
    Jan 2011
    Location
    southern ohio
    Posts
    45
    Post Likes
    Thread Starter
    nope before i started it i put a leash on it

  4. #24
    Join Date
    Mar 2012
    Location
    New Hampshire
    Posts
    84
    Post Likes
    Apology's in advance if this gets too technical for non pro area, feel free to move or delete it. (Like you need my permission... )

    Here is a basic protocol for troubleshooting, I will use a compressor as an example -
    -Talk to the homeowner and get as much info as you can about what happened & when
    -kick on the unit
    -Check the indoor & outdoor unit for anything obvious like loose/broken wires, mice, blown parts, ect.
    -Start digging where you KNOW a component is good (eliminate by testing, not assuming)
    -Work your way down the line until you find a failed component
    -Once you find a problem find out what caused it. Is it wired correctly? Are all the connections solid? (on both ends!)
    -Verify that everything after the failed component is working correctly
    -Stand back & apply power
    -Verify the unit is functioning normally
    -Open the door, get on the floor, everybody walk the dinosaur!

    Example:
    I think I have a bad compressor. First I check the line voltage. If that's good, I kill power & check the contactor. Is it pulled in? Yes. When I remove the LV lead does it kick out? Yes. Then I ohm it, check continuity , and do a visual inspection of it & the wires. Alright, the contactor is good so I'll move on the the capacitor. I mark the wiring connections & pull it out of the unit. First do a visual inspection. Is it bulging, cracked, rusted beyond recognition? No? AWESOME! Grab your meter and check that bad boy out! It's testing good, but before I move on I better check to make sure it's the right size for the compressor. It is - Wicked! Now let's grab the wiring diagram and see if anything is wired "bass ackwards". Ok, wiring looks good, compressor ohm time. It ohms out ok, nothing is grounded, hmm electrically we are all there. I feel like I'm forgetting something....Oh, the fan! Alright, their is a little oil on the shaft but other than that it looks and spins ok. Time for juice! Kick the unit on and take your amp draws on all compressor & fan wires. Amp draws checkout...crap what next? Let's hook up the gauges and see what we get. Holy jeepers Batman! 45 psi suction and 450 psi liquid! I don't think the compressor is the issue! (shooting a mean look at the line drier...You got some splanin' to do Lucy!!)

    Hope this helps! Next time give us more info & check out this link - http://www.grammarly.com/
    Last edited by Tony3696; 10-04-2012 at 08:30 PM. Reason: Added top line


    "I don't know why it be like it is, but it do"

  5. #25
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    excellente'

  6. #26
    Join Date
    Oct 2012
    Location
    Corryton,TN
    Posts
    73
    Post Likes
    may be slow to equalize

  7. #27
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,886
    Post Likes
    I love it when the mods joke around with each other. Shows there not always grumpy old dudes.LOL.
    You need to put the phone down and get back to work!

  8. #28
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,302
    Post Likes
    Quote Originally Posted by jnsrose View Post
    I love it when the mods joke around with each other. Shows there not always grumpy old dudes.LOL.
    Beenthere is the old and grumpy one...... I am the not so much younger and handsome one....

    Although he is the one with the picture of the booth girl last go around

  9. #29
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    First, get your post count up and apply for Pro status, so you can ask techncial questions in the closed Pro forums.

    Second, you mentioned a hard start kit. It that kit uses a PTC, it will not be able to assist the compressor until it has fully cooled off. A potential relay hard start will assist EVERY time. So, you need to find out if you have a good hard start kit there.


    Question: when the compressor fails to start, have you cut the power to the unit and ohmed out the windings? You could be going out on internal overload, so all you will get for resistance is OL.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #30
    Join Date
    Jan 2011
    Location
    southern ohio
    Posts
    45
    Post Likes
    Thread Starter
    thanks for all the info guys had a weak start winding they replaced it with a scroll compressor still had 3 months on warranty. reto kit worked great and was covered also new scroll did not have heater so installed a belly band heater. had to cut reversing valve out made job much easier and quicker

  11. #31
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Quote Originally Posted by rustneversleeps View Post
    had to cut reversing valve out made job much easier and quicker
    Had to cut out the reversing valve??!!
    RVs are a pain to change - 4 pipes as compared to two on a compressor. And RVs are much touchier to braze, especially when you have to lean over the top of the unit to do so.
    I'd much rather change a compressor than a reversing valve.

  12. #32
    Join Date
    Jan 2011
    Location
    southern ohio
    Posts
    45
    Post Likes
    Thread Starter
    hey there ken, I'm mike I worked for O.U. in the a/c shop. Worked with Phil and Cecil

  13. #33
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,903
    Post Likes
    Quote Originally Posted by rustneversleeps View Post
    hey there ken, I'm mike I worked for O.U. in the a/c shop. Worked with Phil and Cecil
    I know them well. We worked together at DWS.

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •