Results 1 to 6 of 6
Thread: Andover Controls
12-03-2012, 09:17 PM #1
New Guest
- Nov 2012
- New York
- 3
Andover Controls
I have about 75 Andover Infinity I2 920 in service. On one of them all the inputs are reading 999.99. I shut the power down and removed the backup battery. I re-energize and reload the controller and I still get the same thing on the inputs. Is this something that is easy to fix or is the board shot and I need a new one.
RGB
12-04-2012, 06:03 AM #2
Thread relocated to the "Controls" section of the site.
12-04-2012, 02:36 PM #3
- Apr 2007
- 3
You might have a high voltage hitting the input buss causing all inputs to read 999. Try unplugging one of the connectors on the buss one at a time to see if that helps. if it does you have a bad input on the connector that is unplugged. I am not sure but my recollection is anything over 10vdc will cause that to happen. Good luck!
Skean
12-04-2012, 10:26 PM #4
New Guest
- Nov 2012
- New York
- 3
Thank you for the reply and the advice. I did what you said one input at a time and still have the problem. I removed all the inputs and the problem did not go away. I powered it down and reset the controller and reloaded it and still have the problem. I guise I will have to buy a new controller.
Thanks again
Roy
12-05-2012, 05:13 PM #5
- Nov 2006
- SE Wisconsin
- 228
Did you also remove any input from the smart sensor input?
How about putting a meter on the inputs and seeing what you have coming in?
A few minutes can save a lot of cash if you haven't tried those yet.
Ken
12-05-2012, 10:01 PM #6
New Guest
- Nov 2012
- New York
- 3