10-03-2012, 08:54 PM #27
york used to put the drier right at discharge on compressor. there are driers rated to handle this but the capacity of the drier drops.
-
10-03-2012, 09:00 PM #28
-
10-03-2012, 10:35 PM #29
Professional Member
- Join Date
- Mar 2012
- Posts
- 91
trane compressor had been changed out by someone who didnt know what they were doing installed liquid line filter drier 6 inches from compressor discharge also cut down the discharge from 1/2 inch into a 163s drier. I got the call for no cooling condenser fan motor had locked up compressor pumped so hard before it went out on overload that it blew the teflon seal out of the roto-lock must have blown a cup of oil out into the unit. please dont install liquid line filter driers in the hot gas discharge line.
-
10-03-2012, 10:38 PM #30
Professional Member
- Join Date
- Mar 2012
- Posts
- 91
not to hi-jack thread but where do you put the liquid line filter drier in a unit with a bi-flow metering device? from the factory i have never seen on installed.
-
10-03-2012, 11:27 PM #31
-
10-04-2012, 12:35 AM #32
Professional Member*
- Join Date
- May 2007
- Location
- Central NJ Area
- Posts
- 646
I've had a lot of leaks on those internally installed (non-copper) filter driers inside condensers on these specific York system in this specific development that are about 6-7 years old. When i check the charge and its quite low the filter drier is the first place i check on these systems then the evap coil.
Why can't you pump down a micro channel style condenser as long as it is not more than the factory charge?
Move the filter drier inside and install approx. 6" from the txv. No rusting and better protection of metering devices.
-
10-04-2012, 08:38 AM #33
-
10-04-2012, 08:41 AM #34
-
10-04-2012, 09:21 AM #35
-
10-04-2012, 10:56 AM #36
unless its a package unit how do you charge to the factory plate
-
10-04-2012, 06:45 PM #37
Charge to the data plate on the condenser, and then add for the line set.
-
10-04-2012, 07:21 PM #38
-
10-04-2012, 08:24 PM #39
Professional Member
- Join Date
- Mar 2012
- Posts
- 91
I am referring to the type of metering device that meters in both directions, one expansion valve for cool same expansion valve for heat. its only on units that would have had a very short liquid line. Water source heat pumps and package units mostly. in this case the liquid line is only really the liquid line in one mode. where to put it?


Reply With Quote