Results 1 to 13 of 39
-
10-01-2012, 07:24 PM #1
Professional Member
- Join Date
- Sep 2011
- Posts
- 58
Replacement compressor wont run.. :(
So I get the call over the weekend to check out a Luxaire R22 system 2.5 ton. Model TCGD30S21S1A with recip compressor.
I get there and the compressor was grounded so waited for today to replace under an almost expired warranty, 2 more months & it would have been no warranty..
Anyway, I check out the nameplate 3.11 lbs factory charge of r22, after installing it I leak tested with nitro and no leaks, pull vacuum and all good, I add 3.14lbs r22 and let it rip... The thing ran great... for about 40 minutes..
It turns out I completely forgot (yes yes, my fault ok?) to change the drier... so I figured np, Ill pull the charge to the compressor and pull another vacuum and thats it right..? not really..
I tried to pull vacuum and the dang compressor didn't suck in the charge, instead it shut down on me and remained like that for about thirty minutes.. All cables hooked up correctly, 24v coming through and 240v enabled, fan was running but comp wasn't.
I had to run to another call and could not come back to this today but I am going back tomorrow..
Could this just be that the compressor overheated and needed longer to cool down run again?
-
10-01-2012, 07:33 PM #2
Professional Member*
- Join Date
- Dec 2005
- Posts
- 1,655
-
10-01-2012, 07:38 PM #3
Professional Member*
- Join Date
- Apr 2003
- Location
- Maple Grove, MN
- Posts
- 713
What does this mean? Are you trying to say that you tried to pump down the unit with it's own compressor, by closing a valve on the liquid line? If so, did you have a gauge on your discharge line to ensure that you weren't overfilling your condenser?
This doesn't have anything to do with it, but is the filter drier before or after the liquid line shut off valve?
-
10-01-2012, 08:00 PM #4
I think those TCGD, whether R22 or the R410a models incorporate micro-channel technology and your not suppose to suck down a system like you would conventionally with the micro-channels, even if it is the factory charge only. I hope you didn't mechanically lock up the compressor with multiple attempts to try to have it smash 15 pounds of salami into a 2 pound bag. I guess a bit of ohm testing at the compressor terminals would let you know if it was out on thermal or if it is locked up.
-
10-01-2012, 08:36 PM #5
Professional Member*
- Join Date
- Apr 2003
- Location
- Maple Grove, MN
- Posts
- 713
-
10-01-2012, 08:45 PM #6
Professional Member
- Join Date
- Sep 2011
- Posts
- 58
-
10-01-2012, 08:54 PM #7
I'm not try to rub it in, but slctech is correct.
There is a service bulletin out from York that says this.........
THE PUMP DOWN OF REFRIGERANT INTO A MICROCHANNEL UNIT IS NOT APPROVED UNDER ANY CIRCUMSTANCE.
This practice can result in damage to the compressor or condenser coil.
The TCGD is a microchannel unit.Instead of learning the tricks of the trade, learn the trade.
-
10-01-2012, 09:06 PM #8
That condenser does have a microchannel coil. York does not approved pumping down a microchannel system.
http://www.fldist.com/applications/D...ems%20York.pdf
Hopefully the compressor is just out thermal overload and hasn't received any damage.
-
10-02-2012, 11:32 PM #9
Professional Member
- Join Date
- Dec 2011
- Location
- somewhere between here and there
- Posts
- 457
just curious if you cannot pump back into microchannel coil.....do they all come dryship? how does the mfg put charge into unit?

Please, Please Please......keep the Factory Smoke in the Wires!!!!!
Is it Rum'Oclock yet???
-
10-02-2012, 11:58 PM #10
Professional Member
- Join Date
- Sep 2011
- Posts
- 58
-
10-03-2012, 12:16 AM #11
The 22 systems come dry. 410 come charged. Ive yet to see a factory charge stamped on a dry charge, York microchannel unit but 3.14 pounds sounds about right so maybe some do.
I know they say not to pump them down but it is possible to pump down as much as the cond will hold. Almost every microchannel ive installed has had to have a considerable amount of refrigerant added. They dont want you attempting to pump them down because they know reefer has been added and that additional reefer will never fit into the condenser. They also know some guys will stand there with the contactor pushed in waiting on it to pump down when the cond is obviously already stacked full
-
10-03-2012, 12:19 AM #12
But Id never attempt to pump one down
-
10-03-2012, 12:23 AM #13
Also curious how you were gonna change the filter drier by pumping it down anyway. All that ive seen have internal driers


Reply With Quote