    R410 air handler with R22 condensing unit

    I will be going back tomorrow for the 2nd time on a new install and would like some help from you pro's!
    I sold a client a 2 ton R22 air handler to go with his 2 ton straight cool XL14i condenser and we mistakenly installed a 3 ton R410 air handler (Trane) and had a call back for not enough cooling the next day. We then replaced the air handler again with the correct size but still using the R410a expansion valve. When I questioned why not replace the expansion valve I was told by management that it will work fine and no need to replace valve. And now after a few days later I find out I am going back and I have a feeling that my problem is going to be that the valve should be replaced to use R22. As I don't really know why other than its wrong. What can I tell my management to explain why it's wrong? And if it is ok to do I will just drop my argument and move on.
    Thank you in advance for your help.

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,808
    It will flood the evap. The pressure in the evap is not high enough to counter the charge in the bulb. The pressure in the external equalizer is what pushes back against the bulb charge. Opposite happens when you use an R22 TXV on an R410A system, it under feeds.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    33,399
    It is going to be the valve. That was made clear by everyone in your last thread on the job.

  4. #4
    Quote Originally Posted by beenthere View Post
    It will flood the evap. The pressure in the evap is not high enough to counter the charge in the bulb. The pressure in the external equalizer is what pushes back against the bulb charge. Opposite happens when you use an R22 TXV on an R410A system, it under feeds.
    Thank you for the answer, i appreciate it.

  5. #5
    Quote Originally Posted by BaldLoonie View Post
    It is going to be the valve. That was made clear by everyone in your last thread on the job.
    I expected an answer like this as well. I realize it won't work correctly but I wanted to know why it won't work correctly. The reason for the new thread was to make it clear to me and drop all the other stuff about the job. So thank you for the useless and obvious info and for taking the time to dig and point out that there was another thread, that really helped!

  6. #6
    Join Date
    May 2009
    Location
    Savannah, Ga/H.H. Island, S.C.
    Posts
    1,278
    Did you install a Trane Hyperion AHU? If so, check the EEV board. There is a dip switch to swap from R410A to R22. No need to change the whole valve or stepper motor.

    Change the switch, cycle the power, and restart.

  7. #7
    Honestly I can't tell you that yet but I am going there in a couple of hours and find out but i believe it is going to be the GAM air handler. Thanks for the input I will check it out.

  8. #8
    Join Date
    Aug 2012
    Posts
    2,329
    What we have here is as failure to communicate.

  9. #9
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,475
    Quote Originally Posted by toocoolforschool View Post
    What we have here is as failure to communicate.
    lol. Some men, you just cant reach

  10. #10
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,475
    I bet the 3 ton ah would have worked by simply changing the txv to r22. The route taken seems backwards to me

  11. #11
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    15,506
    Quote Originally Posted by ar_hvac_man View Post
    I bet the 3 ton ah would have worked by simply changing the txv to r22. The route taken seems backwards to me
    +1.
    __________________________________________________ ____________________________
    “Reality is merely an illusion, albeit a very persistent one.” –Albert Einstein

    “Experience is a hard teacher because she gives the test first, the lesson afterwards.”-Vernon Law

  12. #12
    Join Date
    Jun 2009
    Location
    Upstate SC
    Posts
    1,439
    Quote Originally Posted by ar_hvac_man View Post
    I bet the 3 ton ah would have worked by simply changing the txv to r22. The route taken seems backwards to me
    +2



    Sent from my ERIS using Tapatalk 2

  13. #13
    Seems the problem is the length of the line set. Measured the line set at 375 foot with 10-12 foot vertical rise. Found the liquid line at 67 degrees at the air handler. Spoke with Trane tech support and be said max 200 feet. He said without moving the condenser closer the only other thing I could try is lowering the fan speed which I did and it did help but not a lot. Explained that to the client and of course he gave me "we'll the original system worked fine" so now we are moving the condenser if the lowered fan speed does not work. And the Trane tech support said that having a smaller evap coil is actually helping me.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event