Results 1 to 13 of 36
    Maryland
    RTAA 90 Oil Fault Help!
    I have a Trane RTAA0904XJ01A3C0BG that has circuit 1 continuously tripping due to "Oil System Fault-ckt 1". Now, there has been no recent repairs done to this circuit which could have brought in any contaminates, and the refrigerant charge is good. I'll be going in later to check oil level, but I know the oil filter on this system is generally oversized and shouldn't need replaced regularly (per the mfg), and there doesn't appear to be any leaks on this particular circuit (or even a history of leaks for that matter). Do any of you chiller pro's have any insight as to what a common cause is. I know this chiller verifies proper oil charge by means of the oil temp at the separator and the saturated condenser temp, and I believe it faults after 30 mins if there is lower than a 4 degree difference. What could cause this fault or restriction?
    Jul 2009
    In a mechanical room....
    Fans staging properly?
    Are all of your sensors reading accurately?
    What's your SH/SC
    Do you have a operating Log?
    “It takes courage to grow up and turn out to be who you really are.”
    - E.E. Cummings
    Jun 2012
    Quote Originally Posted by chrishvacman View Post
    What's your SH/SC
    I second that check your condenser fan motors.
    Maryland
    What's your SH/SC
    I'll start with checking that this evening, I was there last week which is why I knew the charge (at that time) was good. However, I just had received emails regarding the faults it was logging, which is what prompted the question. So this could be an issue with condensing temperatures and not so much an oil restriction?
    Jun 2012
    High cond. Pres. Causes a high enough oil differential to trip it. A lot of times one fan falls out and knocks multiple fans out.
    Aug 2009
    Prattville, Alabama
    A search of this site will show numerous threads on this subject. This is not an oil DP switch function. It's usually caused by carry over, or over feeding refrigerant to the evaporator. Check the compressor discharge temp. And look at the temperature sensors that are used to control the EXV. That would be the saturated evaporator refrigerant temperature sensor and the compressor suction temperature sensor. And perform the test on the EXV.
    Jun 2012
    The 125's and lower don't do what i was reffering to do they.
    Aug 2009
    Prattville, Alabama
    Correct, Freightshaker. It's easy to get them confused. I've done it myself. And I ain't gonna promise that I won't do it again!
    Jul 2012
    Western KY
    Sensors being off can cause it. Plugged oil filter could possibly cause it, holding oil in cooler. Never had this fault on the baby screws I take care of so let us know what you come up with.
    Jun 2012
    I'm good at that. Checked a manual after you said that and got to thinking about it. I don't think I have been around a RTAA under 125. Have a safe day NC.
    Keep us updated OP.
    Jul 2009
    Don't forget to check the accuracy of those sensors and DO NOT check that SH and SC with readings from the panel use your own manifold and thermocouple.
    - E.E. Cummings
    Maryland
    An update will be coming in the next couple of hours. Thanks for all the advice it's pointing me in the right direction.
    I also noticed a post earlier where someone was talking about sweating LL canisters on these units possibly caused by bad EEV's. Coincidentally enough this unit does the same when not running (several hours after shutdown is when I noticed it.) So the EEV will definitely be looked at and tested once on site.
    Maryland
    Update: unit is now online, both circuits are running. Here are the readings for circuit 1 (the circuit that has been tripping on 'oil failure').
    Compressor RLA average=91%
    Entering oil temp=125* (actual reading 121*)
    Evap Pressure=68 (confirmed)
    Cond Pressure=251 (actual reading 233 at LL)
    Compressor suction temp=48* (actual reading 52*)
    Evap temp=40*
    Saturated condenser temp=117* (confirmed)
    SH: 14ish
    SC: 9ish
    Those were the readings.
    I ran an EEV test, and it appeared to operate fine, upon opening I saw refrigerant flow in the sight glass, upon closing it stopped.
    Now something odd I haven't heard before was happening, shortly after the chiller started up, on circuit 1 I was hearing a very very high pitched buzzing sound (almost not noticeable), happening for about 5 seconds every 20 seconds or so. Not sure if this info will help anyone but I couldn't pinpoint where it was coming from, just that it sounded to be coming from the two unloader solenoids on the male side?