09-27-2012, 10:41 PM #14
he wants it close to 40*
-
09-27-2012, 10:52 PM #15
I don't think that's going to happen
Unless its. 40F outside
-
09-27-2012, 10:55 PM #16
whys that ?
-
09-27-2012, 11:08 PM #17
You got 4000 btu
You need around 7-8000
On 4 inch walls of insulation
-
09-27-2012, 11:09 PM #18
Your suction psi doesn't seem bad yet your SH is high. Head a little low too. Maybe not enough capacity!!
-
09-27-2012, 11:21 PM #19
If he is your buddy
Try to look for a 2 fan evaporator coil
Then put an used AC condenser
You can get it beer can cold
-
09-27-2012, 11:21 PM #20
i have the txv stem adjusted all the way out and it still has high superheat.
if i dont have enough capacity then this would be a high load.
i thought higher load would be higher pressures. or just higher superheat?
-
09-27-2012, 11:23 PM #21
1.5ton a/c with a 18,000 btu evaporator?
-
09-27-2012, 11:24 PM #22
if u say i can get it 40* then i will get to hookin it up.
-
09-27-2012, 11:27 PM #23
Hvac is rated at 40f coil witch is 1 ton =12000 btu
At 20-25F coil it's approx 7,500 per ton
-
09-27-2012, 11:28 PM #24
You need a real refer coil not AC
2 fan.
-
09-27-2012, 11:35 PM #25
yea, i figured that much. so a 1.5ton r-22 condenser would be about 11500 btus. so i need a 12,000btu 2 fan evap
-
09-27-2012, 11:38 PM #26