    Residential Package unit and Chiller speculation

    I wonder if any of the major mfg's would ever consider modifiying their split systems to be packaged units with split condensers coils only, so you could reheat the air and even do as Ultra-Aire does and use a heat exchanger to increase moisture removal. THen it's jsut a matter of modulating the amount of vapor going ot reheat vs. the condenser coil.... which of course would require EXV's.

    Then again, by the time you've done all that, you might as well just buy a chiller, keep your coil 45F and make hot water for reheat. A chiller eliminates the need for a dedicated dehmidifier, since airflow can be independant of system capacity. I know Crazi is on board with chillers for residential use. Though a WHD is still going ot be a little more economical in a small and medium sized home.

  2. #2
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,939
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    I wonder if any of the major mfg's would ever consider modifiying their split systems to be packaged units with split condensers coils only, so you could reheat the air and even do as Ultra-Aire does and use a heat exchanger to increase moisture removal. THen it's jsut a matter of modulating the amount of vapor going ot reheat vs. the condenser coil.... which of course would require EXV's.

    Then again, by the time you've done all that, you might as well just buy a chiller, keep your coil 45F and make hot water for reheat. A chiller eliminates the need for a dedicated dehmidifier, since airflow can be independant of system capacity. I know Crazi is on board with chillers for residential use. Though a WHD is still going ot be a little more economical in a small and medium sized home.
    If packaged units made sense for homes, there's be more of them out there - it is cheaper to make a packaged unit than a split system. They just don't makes sense the way architects design homes in most cases. If that changes, then yes, a split condenser would make for a very good dehumidifier, especially with a smart control, that way it could seemlessly cycle between cooling mode, and dehumidification mode, while working on the same air stream. That said, since architects DO like split systems (because of freedom of placement), that's the same reason I like chilled water.. :-)

    Whd's do make sense when moisture removal is all you are looking for. That said, if you are wanting to use chilled water for dehumidification, you don't actually HAVE to use hot water for the reheat, you can actually use the chilled water return as the reheat. With two chilled water coils, and a 3-way solenoid valves, you can switch them from cooling only, to dehumidification without cooling.

    I'm still not convinced that chilled water doesn't work in a small/medium sized home. The only reason it doesn't make sense right now is market, not technical. There just isn't enough small chiller systems on the market for their price to drop. You can custom build a small chiller for very cheap - but a mass produced one would be a lot cheaper, and if you subtract the cost of duct installation and go with a couple small fan coils, it is probably not a lot more than a traditional split system. PEX tubing is the key thing that has changed in the market to allow this.

    This exact scenario points to the key advantage of hydronic systems. Once the system's head ends are in place (be it a boiler or chiller), all it takes is coils and valves and that cold/hot water can be manipulated in so many different ways that any comfort scenario can be handled easily.
    Attached Images Attached Images  

  3. #3
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    In my market package units are very common in residential, probably 50+% of homes have package units

  4. #4
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,939
    Post Likes
    Quote Originally Posted by jtrammel View Post
    In my market package units are very common in residential, probably 50+% of homes have package units
    Are those A/C's with gas heat, or heat pump heating? I'm wondering if that is the difference... as I said, around here in SoCal, gas is so cheap, there are very few heat pumps - just about every home has an oversized gas fired furnace, feeding through a split A-coil.

  5. #5
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    I get 18,500 Btus of sensible heat gain and 3,500 Btus of latent gain. I like Ruud/Rheem equipment, and when I look at the specs for their hardware a 2-ton unit does look like enough even for the very hot, humid days we get here in Virginia.
    At 85-F ambient, 75-IDB & 63F IWB a 2-Ton Goodman 13-SEER with just a piston metering device; at 700-CFM, it gets 20,200 total at an S/T of 0.73, or 14,746 sensible & 5,454 latent.

    You need to figure out what the sensible load is at 85-F ambient & how much air infiltration you have; which will also depend on wind conditions & the ambient humidity level at 85-F.

    You also need a room stat that will provide some degrees of temp swing for longer runtime periods; indoor fan should cycle off with condenser & you need a TXV metering device on a 2-Ton evaporator.

    I also agree in general with Teddy Bear's statements...

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Quote Originally Posted by CraziFuzzy View Post
    Are those A/C's with gas heat, or heat pump heating? I'm wondering if that is the difference... as I said, around here in SoCal, gas is so cheap, there are very few heat pumps - just about every home has an oversized gas fired furnace, feeding through a split A-coil.
    probably about 60%gas/electric 35% heat pump 5% dual fuel on residential package equipment

  7. #7
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Package units are typical on older homes in our area that didn't have central heat at the time of construction. Package units aren't used on homes made after 1970 or so in our area.

    The home chiller is VERY interesting. A few other bonuses are when it comes time for system replacement the indoor units don't have to be replaced at the same time as the outside unit. No ductwork looses. Easy zoning. Easy to heat cool additions w/o new equipment. The same water used to cool the space could be used to heat it. Heat could come from heat pump or gas/oil. Whole home dual fuel becomes easy. Domestic hot water could be provided by chiller. Geothermal/Miniature cooling towers become practical. The advantages go on, it's just a matter of somebody coming up with a cost effective unit in smaller sizes.

  8. #8
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,939
    Post Likes
    Quote Originally Posted by 54regcab View Post
    Package units are typical on older homes in our area that didn't have central heat at the time of construction. Package units aren't used on homes made after 1970 or so in our area.

    The home chiller is VERY interesting. A few other bonuses are when it comes time for system replacement the indoor units don't have to be replaced at the same time as the outside unit. No ductwork looses. Easy zoning. Easy to heat cool additions w/o new equipment. The same water used to cool the space could be used to heat it. Heat could come from heat pump or gas/oil. Whole home dual fuel becomes easy. Domestic hot water could be provided by chiller. Geothermal/Miniature cooling towers become practical. The advantages go on, it's just a matter of somebody coming up with a cost effective unit in smaller sizes.
    It would take less innovation than you might think. All it takes to turn a conventional outdoor compressor/condenser unit into a chiller is to connect it to a TXV and heat exchanger (either shell and tube, or brazed plate). The chilled water system itself is also not anything new, as cheap fancoils are already made and readily available in sizes small enough match residential uses, including nice small ceiling mount concealed units, that just need power, t-stat, chilled/hot water, and a condensate drain. Circ pumps, expansion tanks, control valves, are already used in hydronic heating systems. Even conventional hot water tanks makes a very good chilled water buffer tank to avoid excessive chiller cycling. Not the easiest retrofit to an existing home, and some of the savings aren't there, but in a new construction, I don't think I would ever have a home built with conventional ducting at this point.

  9. #9
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Quote Originally Posted by CraziFuzzy View Post
    It would take less innovation than you might think. All it takes to turn a conventional outdoor compressor/condenser unit into a chiller is to connect it to a TXV and heat exchanger (either shell and tube, or brazed plate). The chilled water system itself is also not anything new, as cheap fancoils are already made and readily available in sizes small enough match residential uses, including nice small ceiling mount concealed units, that just need power, t-stat, chilled/hot water, and a condensate drain. Circ pumps, expansion tanks, control valves, are already used in hydronic heating systems. Even conventional hot water tanks makes a very good chilled water buffer tank to avoid excessive chiller cycling. Not the easiest retrofit to an existing home, and some of the savings aren't there, but in a new construction, I don't think I would ever have a home built with conventional ducting at this point.
    My wife used to work at a place that manufactured fan coil units. House I was living at didn't have central heat/air. Got a 600CFM "lab unit" for free and hooked it to the existing gas water heater. The unit had a 5 row coil, 2 rows for hot water, 3 rows hooked to a TXV and a 1.5 ton condenser. System was still in service when I sold the house. Front of the coil is VERY easy to get to on these units, making them easy to clean. The guys at my wife's work thought I was nuts, but were surprised when they saw it work. Now if they would only market to residential customers like FirstCO does...

  10. #10
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,939
    Post Likes
    Quote Originally Posted by 54regcab View Post
    My wife used to work at a place that manufactured fan coil units. House I was living at didn't have central heat/air. Got a 600CFM "lab unit" for free and hooked it to the existing gas water heater. The unit had a 5 row coil, 2 rows for hot water, 3 rows hooked to a TXV and a 1.5 ton condenser. System was still in service when I sold the house. Front of the coil is VERY easy to get to on these units, making them easy to clean. The guys at my wife's work thought I was nuts, but were surprised when they saw it work. Now if they would only market to residential customers like FirstCO does...
    FirstCo only makes DX cooling coil units, no chilled water. Multiaqua makes some great looking units, including full whole-house 4-pipe air handlers to replace a conventional furnace/a-coil setup. This great thing about that particular unit (CWA4) is that it properly does the chilled water coil first, then the blower, then the hot water coil, allowing for dehumidification via simultaneous cooling and reheat.

  11. #11
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Thread Starter
    Quote Originally Posted by CraziFuzzy View Post
    It would take less innovation than you might think. All it takes to turn a conventional outdoor compressor/condenser unit into a chiller is to connect it to a TXV and heat exchanger (either shell and tube, or brazed plate). The chilled water system itself is also not anything new, as cheap fancoils are already made and readily available in sizes small enough match residential uses, including nice small ceiling mount concealed units, that just need power, t-stat, chilled/hot water, and a condensate drain. Circ pumps, expansion tanks, control valves, are already used in hydronic heating systems. Even conventional hot water tanks makes a very good chilled water buffer tank to avoid excessive chiller cycling. Not the easiest retrofit to an existing home, and some of the savings aren't there, but in a new construction, I don't think I would ever have a home built with conventional ducting at this point.
    That's a good point. For R410a, you'd have to get a HE rated for I think around 500psi however... and install the proper PRV if it's rating needs to be lover than the PRV at the compressor.

    I wonder if you could even use an indirect tank as the heat exchanger. Then you'd have an evaporator and storage together. It would hurt efficeincy slightly, since you wouldn't have the higher tmep return water ging to the coil first. Although you'd still have soem stratification in hte tank where hte top of hte tank is warmer than the bottom.

  12. #12
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    That's a good point. For R410a, you'd have to get a HE rated for I think around 500psi however... and install the proper PRV if it's rating needs to be lover than the PRV at the compressor.

    I wonder if you could even use an indirect tank as the heat exchanger. Then you'd have an evaporator and storage together. It would hurt efficeincy slightly, since you wouldn't have the higher tmep return water ging to the coil first. Although you'd still have soem stratification in hte tank where hte top of hte tank is warmer than the bottom.
    Yes, some company makes one, not sure of brand but we installed one at a church for a single fan coil unit when we converted the rest to dx. It was not feasible to get duct to this area and piping was already there. They make the condenser on a stand with the hx and storage tank built into stand, pretty neat set up

  13. #13
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Thread Starter
    Quote Originally Posted by CraziFuzzy View Post
    FirstCo only makes DX cooling coil units, no chilled water. Multiaqua makes some great looking units, including full whole-house 4-pipe air handlers to replace a conventional furnace/a-coil setup. This great thing about that particular unit (CWA4) is that it properly does the chilled water coil first, then the blower, then the hot water coil, allowing for dehumidification via simultaneous cooling and reheat.
    Carrier makes commerical air handlers down to 400 CFM nominal and can be had with chilled water and hot water coils. It looks like they have 2 returns, so you can use up to 100% outside air for economizing. The blower looks like it's after both the chilled and hot water coils. http://www.docs.hvacpartners.com/idc...it/39s-3pd.pdf

  14. #14
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,939
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    That's a good point. For R410a, you'd have to get a HE rated for I think around 500psi however... and install the proper PRV if it's rating needs to be lover than the PRV at the compressor.

    I wonder if you could even use an indirect tank as the heat exchanger. Then you'd have an evaporator and storage together. It would hurt efficeincy slightly, since you wouldn't have the higher tmep return water ging to the coil first. Although you'd still have soem stratification in hte tank where hte top of hte tank is warmer than the bottom.
    Standard Refrigeration sells 'chiller kits', which include the shell and tube evaporator, txv, and controls, that can easily be installed to a standard condenser/compressor unit. they are all rated for R-410A pressures. (http://www.stanref.com/pdfs/CBChille...itBrochure.pdf). I think Alfa Laval also sells kits based on their brazed plate exchangers as well. Thermal Flow (http://www.thermalflow.net/greenm.htm) market a residential chilled water system no idea on the details though. Unico has started marketing a residential chiller system (calling it UniChiller). Many parts of the market ARE starting to take notice - I think the biggeset thing preventing the spread at THIS point is the lack of chiller/chilled-water knowledge of residential techs.

    Quote Originally Posted by motoguy128 View Post
    Carrier makes commerical air handlers down to 400 CFM nominal and can be had with chilled water and hot water coils. It looks like they have 2 returns, so you can use up to 100% outside air for economizing. The blower looks like it's after both the chilled and hot water coils. http://www.docs.hvacpartners.com/idc...it/39s-3pd.pdf
    Of course there are plenty of commercial air handlers using chilled and hot water - the problem is that they are BUILT as commercial units - which means, in most cases, they are way over-built for residential use, and consequently, way too expensive.

  15. #15
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by teddy bear View Post
    Right on. The free cooling can double the amount of moisture removed the compressor verses conventional cooling.
    The heat is 1050 btus per lbs. of moisture removed + 3414 btus per KW used = btus added to the air. The high efficiency of the deh means less heat added to the space. Keep in mind the heat from the dehu only occurs when the properly set up a/c is cycling on/off. So dehu does not add to the cooling unless reheat is needed to extend a/c dehumidification.
    Regards TB
    Now I'm feeling completely lost. It'll have to be dummed down for me to understand. Sorry.

    Quote Originally Posted by motoguy128 View Post
    I wonder if any of the major mfg's would ever consider modifiying their split systems to be packaged units with split condensers coils only, so you could reheat the air and even do as Ultra-Aire does and use a heat exchanger to increase moisture removal. THen it's jsut a matter of modulating the amount of vapor going ot reheat vs. the condenser coil.... which of course would require EXV's.

    Then again, by the time you've done all that, you might as well just buy a chiller, keep your coil 45F and make hot water for reheat. A chiller eliminates the need for a dedicated dehmidifier, since airflow can be independant of system capacity. I know Crazi is on board with chillers for residential use. Though a WHD is still going ot be a little more economical in a small and medium sized home.
    I think Climatemaster offers an optional reheat coil.

  16. #16
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Thread Starter
    Quote Originally Posted by tedkidd View Post
    Now I'm feeling completely lost. It'll have to be dummed down for me to understand. Sorry.

    You have ot think about surface tmepratures of the coil and heat exchanger. FOr efficeincy, you want a big coil area. But to get low dewpoints, you need a small surface area to get lower coil temps. So you put is a propoertionally larger coil, and you end up with lets say 50F surface temps and 55F air discharge. Efficient, but not a very good dehumidifier. Now, what if you flow that air across a heat exchanger and cool it to 55F. Now you flow the incomming air across that coil first. So now you're dropping the dewpoint of the incomming air. Further, that air is now dryer and cooler, so the evaporator will now be even colder, but you still retain that large surface area. The result is that for the same CFM, you will be able to use an even smaller compressor with the same coil size and achieve the same level of moisture removed.

    It's in a sense liek the economizer or the secondary heat exchanger in a condensing boiler or furnace.

  17. #17
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Air path:

    In through HE - the other side of which sees evap exhaust

    Precooled air through evap

    out he as mentioned above

    finally through condensor.

    That it?

  18. #18
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Thread Starter
    Quote Originally Posted by tedkidd View Post
    Air path:

    In through HE - the other side of which sees evap exhaust

    Precooled air through evap

    out he as mentioned above

    finally through condensor.

    That it?
    You got it.

    Or... you needed the air even more dry without much more energy use, you'd add a dessicant wheel and run the incomming air across the condenser coil first to preheat it and drop the RH, then across the regen side of hte dessicant wheel, then the HE, evap, then the dry/regenerated side of the wheel. That would get your dewpoints around 0-20F. Add heat strips for the regeneration and you can see -60F dewpoints.

  19. #19
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes
    Chillers are obviously used EXTENSIVELY in condos / high rises, retail and institutional.

    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  20. #20
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,939
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    Chillers are obviously used EXTENSIVELY in condos / high rises, retail and institutional.
    Of course they are. We're talking about smaller scale though - as in the <6 ton level.

+ Reply to Thread
Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •