    Home Made Chiller with Trane 4TTZ060 Condensing Units

    Hi my name is Javier Borges I am from PR right now I am installing 20 Tons Chilled water system using 4 Trane 4TTZ060 condensing units and 2 10 tons plate HX. Right now I have trouble deciding which DDC Controls to use should I use Trane Controls (++++++++++ Expensive) or my trusted control supplier which supplies Trend Controls. For those of you that do not know these trane units have two compressors inside of them and requiere a special wiring harness to connect them to any control either Trane or Trend. Please reccommend thanks.


    Click image for larger version. 

Name:	20121011_104127.jpg 
Views:	223 
Size:	61.9 KB 
ID:	317091

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Are these the kind of units that have a small compressor and a large compressor?

  3. #3
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Sounds like fun although I'm not familiar with either control systems you mention. Are these units 2 stages? Seems to me like you need something that will the number of stages in addition to a leaving water sensor, freezestat, and all that. How are you going to control the pump? What kind of application is this going to be used it?

  4. #4
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    is it just me or do the txv external equalizer lines look like they are going to the wrong suction line?
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  5. #5
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by jayguy View Post
    is it just me or do the txv external equalizer lines look like they are going to the wrong suction line?
    Has that apearance.


    Pretty cool project though

  6. #6
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    I'm pretty sure those circuits cross over in that BPHE.

    Quote Originally Posted by jayguy View Post
    is it just me or do the txv external equalizer lines look like they are going to the wrong suction line?

  7. #7
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    Looks like a clean job.
    Who makes that pipe isolator for the uni-strut clamp?
    Have you thought of adding a liquid line solenoid valve to prevent migration. Does that condenser have a suction accumulation to prevent liquid slugging on start up or is it even necessary?

    As far as Trend goes they make a good control as long as you have the support.

  8. #8
    Join Date
    Sep 2010
    Posts
    8
    Post Likes
    Thread Starter
    The units are the one that have the double compressor and they are going to be used on high end residence for chilled water. I have already consider a freezestat, and every other sensor in that need to be done. The pumps will be controlled with the same DDC controls that will be installed with DPS and Transmitter for bypass valve. This is my third system that I have built but never with these condensing units. The hx suction and liquid connections are crossed blow them with nitrogen before doing installation.


    Those isolators are electrical PVC Pipe cut at 3"

  9. #9
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    I don't know your condensing unit's exactly but it my understanding that only one compressor runs at a time correct and not a true two stage?

    Quote Originally Posted by jborges View Post
    The units are the one that have the double compressor and they are going to be used on high end residence for chilled water. I have already consider a freezestat, and every other sensor in that need to be done. The pumps will be controlled with the same DDC controls that will be installed with DPS and Transmitter for bypass valve. This is my third system that I have built but never with these condensing units. The hx suction and liquid connections are crossed blow them with nitrogen before doing installation.


    Those isolators are electrical PVC Pipe cut at 3"

  10. #10
    Join Date
    Oct 2006
    Location
    Central Texas
    Posts
    727
    Post Likes
    Interlock your pump with the flow switch and set up a freeze protection. I don't guess it wouldn't much matter what controls you use. As far as staging goes, looks like x controls will just bring on more compressors in order to compensate for the load. Good stuff.
    Last edited by txhvac; 10-14-2012 at 08:34 PM. Reason: Wrong spelling
    Sic Semper Tyrannis.

  11. #11
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    So you are looking at 9 binary outputs, 2 binary inputs, 5 analog inputs, 1 analog output. Are you isolating the heat exchangers from each for low load conditions? Did you provide head pressure controls on the condensing units? How about a flow meter instead of DP?
    UA Local 141

  12. #12
    Join Date
    Oct 2012
    Location
    Israel
    Posts
    4
    Post Likes

    4 stage control + fan

    The fan contact will run the water pump. Hopefully the condensing units are equipped with essential safety
    devices and solenoid valves( not essential in this kind of a system). Make sure the the pump
    is off delayed. Cheers

  13. #13
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Quote Originally Posted by Letonil View Post
    The fan contact will run the water pump. Hopefully the condensing units are equipped with essential safety
    devices and solenoid valves( not essential in this kind of a system). Make sure the the pump
    is off delayed. Cheers
    There is more then four stages here, each condensor has two stages.
    UA Local 141

  14. #14
    Join Date
    Oct 2012
    Location
    Israel
    Posts
    4
    Post Likes

    Sorry, I didn't notice

    Quote Originally Posted by berg2666 View Post
    There is more then four stages here, each condensor has two stages.
    Anyway, you can use an aditional 4 stage simple thermostat. Don't worry about the head pressure control
    of the comps. it's probably in the condense units.
    I forgot to mention that you must install a seperate water pump with a check valve on the discharge side
    for each heat exchanger and please don't forget the safety devices such as water flow switch and freeze protector
    for each heat exchanger. Cheers

  15. #15
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Quote Originally Posted by Letonil View Post
    Anyway, you can use an aditional 4 stage simple thermostat. Don't worry about the head pressure control
    of the comps. it's probably in the condense units.
    I forgot to mention that you must install a seperate water pump with a check valve on the discharge side
    for each heat exchanger and please don't forget the safety devices such as water flow switch and freeze protector
    for each heat exchanger. Cheers
    And your thoughts on the bypass valve???
    UA Local 141

  16. #16
    Join Date
    Sep 2010
    Posts
    8
    Post Likes
    Thread Starter
    I am using a DDC based control system because it gives me the best control of the system, and the fancoil units in the house. I already have done all things for protecting the system including: freezestat, dp switch (is more accurate than a flow switch), on/off control valves for HX when full load is not neccesarry, planning on putting high and low ref pressure sensors to communicate to the controler. These CU start using the big compressor and when the load is acheived the small compressor starts that is the way the units saves energy. The thing with the CU is that if you do it wrong the compressors start failing and after a couple of failures Tranes does not warranty them at least locally this is my main problem. Have known of this problem from an early experience from another contractor but the system was with a multiple cu units split system.

  17. #17
    Join Date
    Oct 2012
    Location
    Israel
    Posts
    4
    Post Likes

    what bypass?

    Quote Originally Posted by berg2666 View Post
    And your thoughts on the bypass valve???
    What bypass valve?

  18. #18
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    929
    Post Likes
    Looks like fun, sounds like you've got it covered. Ive done a few retrofits but never just built my own chiller.
    Let us know how it turns out.

  19. #19
    Join Date
    Sep 2010
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by Letonil View Post
    What bypass valve?
    Due to the system been built with two way control valves the system needs a bypass with a proportional control valve to relieve system pressure when valves start to close.

  20. #20
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Quote Originally Posted by Letonil View Post
    What bypass valve?

    Please read the whole post and you will find mention of a bypass valve.


    You will find out that if you come to this forum and only read the first post and then comment without reading all that your opinion will eventually become null and void because people will learn that you are not paying 100 percent attention to what you are reading.
    UA Local 141

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •