    I've read some posts where guys have said they rarely ever hook up gauges to units for fear of loosing refer but some of you guys still manage to get your sc and sh readings. How is that ? And if you don't take pressure readings how do you really know whats going on? Is there some trick cause I've never heard of it.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,661
    Post Likes
    Quote Originally Posted by canusayinsanity View Post
    ...Is there some trick cause I've never heard of it.
    nope. unless the unit has unit mounted gages (which never seem to be accurate) or unit mounted pressure transducers (which are rarely on the liquid line), i don't see how that would be performed.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  3. #3
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,439
    Post Likes
    Quote Originally Posted by jayguy View Post
    nope. unless the unit has unit mounted gages (which never seem to be accurate) or unit mounted pressure transducers (which are rarely on the liquid line), i don't see how that would be performed.
    think about a chiller with thermistors only, no pressure transducers,the module translate temperatures to pressures for you perusal, plenty of them out there.

  4. #4
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,661
    Post Likes
    Quote Originally Posted by valdelocc View Post
    think about a chiller with thermistors only, no pressure transducers,the module translate temperatures to pressures for you perusal, plenty of them out there.
    i know exactly what you are talking about...keep in mind that you are assuming that the refrigerant is ONLY the nameplate refrigerant and that there aren't any non-condensibles, no water tube leaks, etc. but if we are going to just go around assuming things, then why do the customers need us? my wife assumes plenty of things about me that aren't true either.

    if you are the only one taking care of the unit, then perhaps you can use the two temperature method. but even chillers that use only thermistors have problems too when the therminstors go bad and the unit doesn't know it.

    also think about what you are missing. gages will show pressure swings much faster than waiting for the txv to stabilize and give you solid temperature readings that will tell you accurate information.

    i am not against the 2 temperature method...it has limitations and in some cases, very serious limitations.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  5. #5
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,160
    Post Likes
    I use my digicool ak900. have hoses with ball valves. after i take my readings i close the ball valves, remove both hoses from ports and hook liquid line hose to suction valve and suck it back in. on PM's my company says check temp split. i have seen plenty of units with good deltas but overcharged, undercharged, bad txvs, etc.....

  6. #6
    Join Date
    Aug 2012
    Location
    west burbs,il
    Posts
    177
    Post Likes
    Gravity I read you jumped into commercial, first time? Welcome to chaos.. Where do you get the ak900, I wouldn't mind seeing it in person at supply house.

  7. #7
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    5,160
    Post Likes
    Its not all that bad.

    We do a lot of RTU's. Very easy to work on because everything is all in one.

    I worked on some commercial things when doing residential. It's all the same but more crap packed into one.

    It is fun though. Got to replace a 7.5ton compressor in a 15ton split a/c. added some 1-5/8 and 7/8 ball valves with a new suction shell.

    You can get the ak900 from trutechtools.com. Enter hvactalk as a code and get 10% off.

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,439
    Post Likes
    Quote Originally Posted by canusayinsanity View Post
    but some of you guys still manage to get your sc and sh readings. Is there some trick cause I've never heard of it.
    yeah there is a trick and all you need is a good thermometer, refrigeration guys do it all the time.

  9. #9
    Join Date
    Dec 2000
    Location
    phoenix, arizona
    Posts
    1,148
    Post Likes

    yes, it can be done

    Quote Originally Posted by valdelocc View Post
    yeah there is a trick and all you need is a good thermometer, refrigeration guys do it all the time.
    Many years ago, I worked on an RTU on top of a large outlet store shopping center. While I was there, the in house shopping center maintenance supervisor stopped over to chat with me.

    He carries a tiny tool bag, and a CPS temp seeker TM250. ( a four station multi-port Digital thermometer), No manifold gage. He showed me how to check charge with temperature only.

    Basically, he hooked up a temperature probe to discharge port at the compressor, a probe at bottom of condenser, temp probe at Suction (maybe 1-2 feet from the compressor).). He could tell if it system is over charged, or under charge. His word to me was: temperature, temperature, temperature. He would say something like ; this one is probabbly two pund short, this one is probably 3 pound short. by garr ...lly, he was right on the money.

    I ask him why he doesn't take care it himself; His reply was; if the shopping center knew he can do all these stuff, they simply add xtra work without more compensation. So they always hire an outside contractor.
    Decide what you want, decide what you are willing to exchange for it. Establish your priorities and go to work." H.L. Hunt

    "In order that people may be happy in their work, these three things are needed: They must be fit for it. They must not do too much of it. And they must have a sense of success in it." John uskin

  10. #10
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,207
    Post Likes
    *

  11. #11
    Join Date
    Aug 2012
    Location
    west burbs,il
    Posts
    177
    Post Likes
    l've talked to a couple top refer guys and they said its impossible to get your readings unless your getting pressures and line temps. So unless you get your pressure reading I just don't see it happening.

  12. #12
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    2,439
    Post Likes
    Quote Originally Posted by canusayinsanity View Post
    l've talked to a couple top refer guys and they said its impossible to get your readings unless your getting pressures and line temps. So unless you get your pressure reading I just don't see it happening.
    I think you need to re-examine your definition of "top refer guy"
    I had compared both methods and they come within the margin of error, the tricky part is knowing where to measure, there are plenty of thread on the subject, do a little research.

  13. #13
    Join Date
    Jan 2010
    Location
    Toronto,Ontario Canada
    Posts
    394
    Post Likes
    First off When you go to a job site the last thing you do is put your gauges on. You make sure everything else is running up to par. (visually inspect the unit first) things like belts,filters,coils,fans and of course your electrical components and then if you still have a problem then put ur gauges on. usually when you do put ur gauges on u lose a little refrigerant and of course you gotta put it back,especially in refrigeration. My boss went over this stuff when i first started and i said the same thing, but i get it now why you should never put ur gauges on right away. it takes time but it works a lot better. i dont know if most of you guys will agree with what im saying.

    And of course have a few reliable thermometers on you all the time Just like the other guy said.
    (yeah there is a trick and all you need is a good thermometer, refrigeration guys do it all the time)-valdelocc
    Last edited by akelesis; 09-27-2012 at 03:19 PM.
    Get er Done!

    Do what has to be done
    when it has to be done
    as well as it has to be done
    And doing it all the time.