mitsubishi mr slim restriction
well first let me say that Im not sure if this the right place to post my question, I've posted a couple of questions on this site before, but its been awhile so..I often read on this site whenever I get spare time, but rarely post anything. anyways
Question: anyone ever come across a mitsub mr. slim with a restriction?
if so how/ what did you do to repair?
a little info; Im getting error code P8-"abnormality in outdoor unit" 210 hi side /60 true suction + only 65psi @ transphase port, (the access @the service valve) I was told by the mitsub. tech support guy I should have about 100psi there! superheat of about 39, supply air 66 return of 75
Any help sugestions will be greatly appreaciated, thanks
-
09-28-2012, 07:42 PM #2
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 941
They are notorious for liquid line restrictions, there is a small bulb with a strainer inside in the liquid line before the metering device, cut it it and replace it with a regular dryer.