    Airflow? Unit have a belt drive blower? Have you tried heating up the expansion valve bulb with your hand to see if it will react at all?
  2. #28
    May 2011
    tallahassee,fl
    Need sub cooling measurement now to further diagnose.
  3. #29
    Aug 2012
    North Dakota
    yes in my world w/ txv you should be charging to subcooling
  4. #30
    Apr 2012
    winnipeg
    its still not right ...,..getting better though
  5. #31
    Jul 2009
    Columbia, MD
    bad txv or clogged drier
  6. #32
    Sep 2012
    Melbourne, Australia
    Standing pressure of R22 of 200 PSI sounds a little high to lil old me. I'd expect more like 90-100 equalised. Would try rto reclaim some juice and see what happens to prove over charged thoery, before jumping to conclusion of a dead TXV. Could be non condensables too if someone doesn't consider a vacc pump worthy If it is over charged after taking some juice out, reclaim the lot just incase of non condensables, throw in a new liq drier, vacc the lot out way down low and crage her again. This time make sure the ambient is high enough or block some condenser not to over charge her. Head pressure is relative to suction!
    Assuming the obvious,the fan is running, and there is no other valve between high side and low side which might be DOA, closed blocked. TXV could then be the only blockage. Those ball valves are open right?
  7. #33
    Apr 2012
    winnipeg
    oh boy .... i am going to bed
  8. #34
    Jul 2009
    Columbia, MD
    i know......i know.....
    90-100psi standing is ~ 60* outside temp.
    the OP never told us what the outdoor ambient is.
    also, whats this head pressure is relative to suction stuff?
  9. #35
    What's the subcooling?
  10. #36
    Change the TXV
  11. #37
    Oct 2007
    Austin Texas
    Missing way too much information to try to help. Besides this is the resi section. Who has a ten ton unit at their house?
    Nemo me impune lacessit.
    How much blood do I have to bathe in to get clean?
    Don't look down on anyone unless you're helping them up.
  12. #38
    May 2012
    Now it seems to be running right but can't lower low side line temp, its about 76degrees coming into the compressor.
    I don't see any insulation on your compressor suction line in that photo.
  13. #39
    Tallahassee, FL
    Quote Originally Posted by John Culpepper View Post
    I do. Jk
    but its a two stage so I have that "extra " little bit you know.