    Fans on? Plastic bag wrapped around cond? Split coils? If fans on and coils clean start pulling charge. Agree with push it on the restriction thing

  2. #15
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,031
    There must be 50lbs in that thing maybe more. Way overcharged. Once removed she should run longer so you can begin to diagnose it.

  3. #16
    Join Date
    Nov 2005
    Location
    Texas
    Posts
    1,628
    Quote Originally Posted by myhvacx View Post
    Attachment 312091
    Reciprocating compressor, the compressor is about 3 months old, the air h is about 3 years old, there's a pic, hope it uploads.. The system may have been overcharged from what i understand about 2 weeks ago..
    Standing high side reads 200psi.
    Unless it is 100° where you are, that 200psi standing points to non-condensables......Just a thought.

  4. #17
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Overcharged severely if hp trip that quick. Pull some juice.

  5. #18
    Join Date
    Jul 2008
    Location
    Mid Michigan
    Posts
    319
    Quote Originally Posted by gonefishing View Post
    Unless it is 100° where you are, that 200psi standing points to non-condensables......Just a thought.
    Exactly what I was thinking.
    Waddya mean don't thaw out the frig with a knive?

  6. #19
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,595
    I vote for overcharged also but I bet there's another problem lying in wait also. Like maybe someone gassed it up more to keep the suction pressure up.

    Were you the one who changed the compressor?

  7. #20
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,836
    unhook compressor and let condenser fan run and watch the high side pressure. or verify that both sides are equal pressure. where is the filter drier? i had one restricted so bad not too long ago that the compressor hit 600 psi in 20 seconds

  8. #21
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,337
    Pull charge. Change drier. Start over.

  9. #22
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,836
    and while your at it. weigh what you took out

  10. #23
    Join Date
    Sep 2011
    Posts
    58
    It was actually way overcharged, so that solved high pressure 5 second run issue..

    Now it seems to be running right but can't lower low side line temp, its about 76degrees coming into the compressor.

    So right now my superheat is around 60, which is very high, I have reached 250psi on the high side while unit is running but the suction does not seem to be affected, remains at around 40psig.

    I think this is what the previous person that worked on it had, so whoever this was just kept on adding freon.

    RIght now my big issue is calibrating it correctly but just don't want to end up overcharging it like the last person did..

  11. #24
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    518
    whats your metering device and what charging method are u using

  12. #25
    Join Date
    Sep 2011
    Posts
    58
    Quote Originally Posted by mechanical'al View Post
    whats your metering device and what charging method are u using
    TXV, charging on low side.

  13. #26
    Join Date
    Aug 2012
    Location
    North Dakota
    Posts
    518
    to sub cooling??? what is your sub cooling????

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event