High pressure problem
Troubleshhoting a 10 to r22 system w reset switch, upon resetting it the pump turn on and high side hits 400psi in a few seconds then shuts off..
When it shuts off the txv valve makes a strong humming noise for a few seconds then stops... Could this be a bad txv?
-
09-26-2012, 02:33 PM #2
-
09-26-2012, 02:39 PM #3
I think he meant 10 ton r22 system.
Sounds like a ristriction of the collosal{big} type.
-
09-26-2012, 02:39 PM #4
Regular Guest
- Join Date
- Aug 2012
- Location
- Vancouver Island, British Columbia
- Posts
- 16
think he means 10 ton maybe. if you think it is the tx put the bulb in some warm water and see if that makes a difference. check for any visible kinks in line, possible plugged filter drier? how many "seconds" does it take
-
09-26-2012, 02:40 PM #5
Regular Guest
- Join Date
- Aug 2012
- Location
- Vancouver Island, British Columbia
- Posts
- 16
woops looks like im being a parrot
-
09-26-2012, 03:06 PM #6
Professional Member
- Join Date
- Sep 2011
- Posts
- 58
Five seconds , yes i meant 10 ton
-
09-26-2012, 03:13 PM #7
Professional Member
- Join Date
- Jun 2012
- Location
- Northeast
- Posts
- 120
it can't be the TXV. You would get more then 5 seconds of run time. And it would need to be overcharged, the unit should pump down and trip the low pressure before it trips the HP switch. Is it a tin can or semihermetic? Where is the pressure switch? Are there any service valves on the dischargre line that can be partially closed? What is the history of the equipment?
-
09-26-2012, 03:13 PM #8
Professional Member
- Join Date
- Sep 2011
- Posts
- 58
Just put the bulb in warm water, no difference..
-
09-26-2012, 03:19 PM #9
Professional Member
- Join Date
- Sep 2011
- Posts
- 58
Reciprocating compressor, the compressor is about 3 months old, the air h is about 3 years old, there's a pic, hope it uploads.. The system may have been overcharged from what i understand about 2 weeks ago..
Standing high side reads 200psi.
-
09-26-2012, 03:19 PM #10
Professional Member
- Join Date
- Sep 2011
- Posts
- 58
Im sry, scroll not recip..
-
09-26-2012, 03:34 PM #11
If there has been a compressor change on the unit I have seen the needle in the txv black and dirty from the torching/old compressor burn out. Especially when brazing without nitrogen.
-
09-26-2012, 03:38 PM #12
Fans on? Plastic bag wrapped around cond? Split coils? If fans on and coils clean start pulling charge. Agree with push it on the restriction thing
-
09-26-2012, 03:55 PM #13
what was the old comps. problem ??? contamanents ,no nitro purge, heavy braze,didnt replace drier ,didnt add temp suct. drier ?????