Using old tubing with new 410a equipment
What are the results of using old tubing from an R-22 system that is being converted to 410A? I have been able to use new tubing until now, where it is very impractical. Supposedly you can flush the existing tubing to remove the mineral oil. What have been the results in the real world?
-
09-21-2012, 12:41 AM #2
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,658
unless theres somehow an excessive amount of oil in the lines, you don't need to do anything different than you would if swapping out R-22 equipment. mixing the oils doesn't create some sort of super sludge like the flush companies want you to believe.
-
09-21-2012, 08:22 AM #3
Regular Guest
- Join Date
- Sep 2012
- Location
- Harrisburg, PA
- Posts
- 12
Make sure you confirm the size of the line set!!! also make sure you use the flush.
-
09-21-2012, 09:07 AM #4
I worry more about the flushing agent than I do the oil so I dont flush unless its a burn out.
-
09-21-2012, 09:51 AM #5
Regular Guest
- Join Date
- Sep 2012
- Posts
- 11
Experience counts. You guys feel like this is a concensus everywhere? If your experience and that of your peers tells you that there are more imprtant things to worry about, then I won't get too concerned about it. They said a lot of things about 410A in the beginning. I like this one: Do not charge vapor. Do not top off. Then they report that testing has shown that a leaking system can be topped off something like 35 times with no noticeable effect. Love the internet.
-
09-21-2012, 10:15 AM #6
New Guest
- Join Date
- May 2011
- Location
- Pennsylvania, USA
- Posts
- 4
Just verify the line sizes are correct for the new equiptment. Do a tripple evacuation.
-
09-21-2012, 11:27 AM #7
Don't forget to change FD.
-
09-21-2012, 05:59 PM #8
Make sure line set size is ok. Then blow it out with nitro.
Its still best to only charge r410a as liquid only.
The false rumor you heard about not topping off was from sourves that either didn,t have any training on it, or were just prejuctice against it.
-
09-21-2012, 10:56 PM #9
Regular Guest
- Join Date
- Nov 2011
- Location
- Phoenix,AZ
- Posts
- 96
nearly all the linesets here are behind drywall so replacing them is not an option not to mention most people wont pay extra for them to be replaced.
-
09-21-2012, 11:13 PM #10
I just blow with nitro and pull a good vac with a micron gauge. When we first started installing 410 we used the flush but I feel like it will do more harm than a little oil. That flush is some potent stuff, smells like nail polish remover and burns your eyes. Trane install manual says to NOT use ac flush
-
09-21-2012, 11:23 PM #11
how would trane know.... lol
it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair
-
09-22-2012, 08:27 PM #12
Regular Guest
- Join Date
- Feb 2007
- Location
- joliet il.
- Posts
- 3
I would make sure there are no soft solder joints in it first!Back in the day , alot of installers used 50/50 or 95/5 on there joints! 410a pressures may cause a failure at this type of joint! Nitro flush is is a minimum prep.
-