Results 1 to 13 of 15
    May 2012
    MasterBilt walk in cooler issue
    I was working on a masterbilt walk in cooler r-22 dual evaporator ive been there 2 times manager says it wasn't cooling when he gets in but everytime ive been there it was down to temp. I thought it might be the defrost set for too long it was originally set for 12am and 12pm 45mins in defrost so i set it for 25mins defrost then i got called back on sunday and temp was 57 degrees and not droppping my condenser was running i had a 10 suction and a 150 head i checked my pipe temp at oulet of both evaps it was 56 degrees so i thought maybe my liquidline solonoid might be having issues so i took the temp on the inlet and out let i was getting 92 degrees, and checked if my solonoid was gettig voltage and energizing it was so i added some refrigerant to see if pressures went up i added 5oz of refrig and my compressor made a noise like it had a high load and then my pressure went to normal had 45 suction and 180head and started cooling the box down i dont think it was low on charge does anyone have any ideas what could be going on? i have a feeling ill be getting that call back im an a/c guy and new to refrig and advice is greatly apperciated
    Nov 2009
    Richmond, working under tarps
    model and serial #?
    May 2012
    model mhhx030ccc serial 0j434834 it has can coil thermal corp evaps
    May 2012
    0s434834 sorry cant read my own handwritting
    Was it a cold morning when you went back?
    Sent from my SCH-I800 using Tapatalk 2
    May 2012
    eh not really it was in the 70s its weird cause i was there 3 days prior and i was getting good pressure and it was around the same outside temp
    Oct 2011
    Chicagoland Area
    Low on charge
    Jul 2011
    Lehigh Valley, PA
    Adding 5 oz to a system holding better than 5lbs? Are you sure there are no loose connections on the solenoid wiring? Or the dual pressure switch could be out of adjustment or faulty in some way? The Ranco should DE-enegize the NC solenoid thus pumping the compressor down to about 10psi, and this should de-enegize the compressor contactor. I'd check to see how low this compressor will pump down too.
    Jul 2010
    So-Cal
    Low on charge
    Does this unit have a sight glass?
    Mar 2009
    Mid-Mo
    Quote Originally Posted by jackintheboxtec View Post
    X3
    NH
    Yep add the winter charge to this thing...... It's starting to get cold at night and will need to flood the condenser to operate properly.. If it has a headmaster that is.
    Nov 2009
    It should
    c/p
    Finish Charging Procedures
    A. Preliminary
    1. Be sure all service valves are “open”.
    2. Loosen the compressor hold-down bolts and remove shipping clips to allow compressor to
    float freely on the springs.
    3. Check evaporator fan motors after start-up. Medium temperature, air defrost fans run
    continuously. Low temperature fans and coolers provided with electric defrost will be
    delayed by the fan control.
    11
    4. Start the system by “flipping on” the circuit breaker in the unit electric box.
    5. Start charging per (B), (C), (D) or (E) on the following pages.
    CAUTION: Never add liquid refrigerant to the suction side of the compressor.
    6. Check operating pressures while charging and on initial pulldown to prevent damage if a
    problem occurs. If system “floods” back to the compressor, adjust the thermostatic expansion
    valve as required for proper operation. There should be at least +30F superheat
    entering the compressor.
    7. Observe compressor amperage draw and compare to compressor nameplate to prevent
    damage due to high amperage. The oil sight glass should be between 1/2 and 3/4 full
    during normal operation.
    B. Remote "M-Series" Condensing Units
    1. For models without head pressure control valve: With the system operating, add
    refrigerant until the sight glass indicates a full charge, then add one pound for each 2 rated
    horsepower of the condensing unit when charging above +75F. If ambient is below +75F,
    add 1/2 to the above. See A.6 above.
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by Capz View Post
    The 5oz he added was just enough to get the headmaster to kick in.
