Thread: Problem with Trane XR15

  1. #61
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    I'm not saying the guy is a bad tech, sometimes we don't get it right the first time and have todo more trouble shooting .personally I would not keep spending money on other companies I would make the company that installed fix it or remove it with a refund.
    Oh ok. Sorry if I took that a little too serious. Thanks for the point. I've been so busy lately so I haven't had a chance to call anyways. I will probably contact this company back, and we'll see how it goes from there.

  2. #62
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by Rodney28334 View Post
    X2 Also, looks like the refrigerant lines between the wall and heatpump have some mean looking bends, but hard to tell from that angle.
    I would agree that the refrigerant lines do have some big bends, but I'm surprised that the tech never mentioned anything about it.

  3. #63
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    I'm not saying the guy is a bad tech, sometimes we don't get it right the first time and have todo more trouble shooting .personally I would not keep spending money on other companies I would make the company that installed fix it or remove it with a refund.
    And also, the company who did our tune-up is the company we have always been using for years. The company who installed the unit was the first time we ever used them. So I should the call them instead of the company who did the tune-up.

  4. #64
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    Why did you not have the company that you have been using for years install your new system. If the installer can't figure it out have them call there tech rep to come help them as you should not have to keep paying to get it right

  5. #65
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    Why did you not have the company that you have been using for years install your new system. If the installer can't figure it out have them call there tech rep to come help them as you should not have to keep paying to get it right
    The reason why we used a different company to install the system was because they work with home depot. Home Depot had a financing special so that's why we used them. I do really wish that we had the company that we have been using for years install our system because I think it would have been a lot easier instead of having to deal with two separate companies. The one we have been using for years is a Lennox and Amana dealer, which I have no problem with that. Plus, they installed our new upstairs system a few months ago (the new A/C in early April, the new furnace in mid July)

  6. #66
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by crmont View Post
    I hate to agree with Ryan but after looking at the pictures a little closer, it appears that there is a 16x20x1 air filter in place and it might even be an "allergy free" type filter. The return duct is also cut in one side of the furnace which historically makes for low airflow. Also the indoor coil looks suspiciously small for a 15 seer 3.5 ton. Please post the model numbers of the indoor coil and the Lennox furnace so i can verify the match up. Finally, have the static pressure checked and compared to the blower data. If the blower data isn't available, the furnace model number will clarify. Thanks.
    I just remembered something. My son wants to be an HVAC tech when he gets older and he and I were watching the tech inspect the furnace and I noticed that the opening of the return plenum that's connected to the side of the furnace is actually cut like a circle that's the same size as the blower and not a cut rectangle that matches the size of the return plenum. If you know what I mean. The tech never mentioned anything about that. The new upstairs furnace does have a cut rectangle that is in the whole lower part of the side of the furnace that's connected to the return plenum.

  7. #67
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Quote Originally Posted by 545GAlady View Post
    I just remembered something. My son wants to be an HVAC tech when he gets older and he and I were watching the tech inspect the furnace and I noticed that the opening of the return plenum that's connected to the side of the furnace is actually cut like a circle that's the same size as the blower and not a cut rectangle that matches the size of the return plenum. If you know what I mean. The tech never mentioned anything about that. The new upstairs furnace does have a cut rectangle that is in the whole lower part of the side of the furnace that's connected to the return plenum.
    May or may not be an issue depending on the size of the "hole." Again, you need a tech that can quantify the actual CFM you are getting by properly measuring ESP. For a 3.5 ton unit, your target would be 1400 CFM. It's doubtful that the total filter surface area is being used with a setup like you describe. Also, it's hard to tell from the pictures, but the flex duct may be marginal for 3.5 ton (with a standard, non-variable PSC motor at least), especially if there are lots of bends. Can you give us sizes (in. dia) and approximate run lengths?

  8. #68
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by RyanHughes View Post
    May or may not be an issue depending on the size of the "hole." Again, you need a tech that can quantify the actual CFM you are getting by properly measuring ESP. For a 3.5 ton unit, your target would be 1400 CFM. It's doubtful that the total filter surface area is being used with a setup like you describe. Also, it's hard to tell from the pictures, but the flex duct may be marginal for 3.5 ton (with a standard, non-variable PSC motor at least), especially if there are lots of bends. Can you give us sizes (in. dia) and approximate run lengths?
    Thanks for the input. I'll see if another tech can look at that. The whole system has 16 supplies and 7 returns. The 2 supplies in the main living room are 8 inch and the two supplies in the master bedroom are 6 inch. The master bedroom has 1 return. I will need to find out the run lengths of the ducts. The office has a 8 inch supply and 2 returns. The main hallway has two returns and the dining room has 2 returns as well. The other supplies are pretty much 6 inch (2 of the ones in the kitchen) and the rest are 4 inch (I think). The returns are all 8 inch. Before the heat pump was installed, the contractor did do a load calculation and said 3.5 tons was enough, which I already mentioned in my very first post in this thread. Hope this helps.

  9. #69
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Quote Originally Posted by 545GAlady View Post
    Thanks for the input. I'll see if another tech can look at that. The whole system has 16 supplies and 7 returns. The 2 supplies in the main living room are 8 inch and the two supplies in the master bedroom are 6 inch. The master bedroom has 1 return. I will need to find out the run lengths of the ducts. The office has a 8 inch supply and 2 returns. The main hallway has two returns and the dining room has 2 returns as well. The other supplies are pretty much 6 inch (2 of the ones in the kitchen) and the rest are 4 inch (I think). The returns are all 8 inch. Before the heat pump was installed, the contractor did do a load calculation and said 3.5 tons was enough, which I already mentioned in my very first post in this thread. Hope this helps.
    I was more curious of the size of the ducts coming off the supply and return plenums at the furnace, which I assume serve distribution boxes (?). Not atypical for new construction installations.

  10. #70
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by RyanHughes View Post
    I was more curious of the size of the ducts coming off the supply and return plenums at the furnace, which I assume serve distribution boxes (?). Not atypical for new construction installations.
    Oh Ok. Sorry for not giving that info. I will measure the sizes coming off of the supply and the return plenums.

  11. #71
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    I'm probably wrong about the sizes, but here's the results:

    Supply plenum:10 or 12 inch trunk (I think), 10 inch trunk, two 8 inch runs, and two 4 inch runs.
    Return plenum: Two 8 inch runs and a 12 inch trunk.

    I'll have the tech look at the ducts to properly measure them.

  12. #72
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    And I had a mistake on the number of supply vents. There's actually 17 supplies NOT 16.

  13. #73
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Quote Originally Posted by 545GAlady View Post
    I'm probably wrong about the sizes, but here's the results:

    Supply plenum:10 or 12 inch trunk (I think), 10 inch trunk, two 8 inch runs, and two 4 inch runs.
    Return plenum: Two 8 inch runs and a 12 inch trunk.

    I'll have the tech look at the ducts to properly measure them.
    I'll assume you measured them properly, and offer you my opinion that you are certainly short on return. With a standard blower, a conservative estimate would be 450-500 cfm through the 12" flex return and 150-200 cfm through the 8" flex returns, assuming average length runs without sharp bends. Definitely low for a 3.5 ton system, so I do think you are either low on airflow, overcharged, or both. I would definitely recommend ensuring properly airflow and then going back to have the system properly charged per subcooling. Without the proper airflow, you aren't getting full capacity or efficiency. A 3.5 ton system doesn't necessarily need 1400 cfm, but I would at least aim for 1225 CFM (350 cfm/ton). Your furnace should have a blower chart showing the airflow provided at various external static pressures. Since it's a standard, non variable-speed blower, it probably has a maximum static of 0.5" or less (at which it is capable of delivering rated airflow), which you may be over already. There is no set amount of airflow that one size duct can handle, so it is important that you get the static pressure checked (for example, I have a 6" flex return in my basement -- short, straight flex run right off the return plenum pulling 200-250 cfm verified using a balometer).
    Last edited by RyanHughes; 10-03-2012 at 11:37 PM.

  14. #74
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by RyanHughes View Post
    I'll assume you measured them properly, and offer you my opinion that you are certainly short on return. With a standard blower, a conservative estimate would be 450-500 cfm through the 12" flex return and 150-200 cfm through the 8" flex returns, assuming runs that aren't too long and without sharp bends. Definitely low for a 3.5 ton system, so I do think you are either low on airflow, overcharged, or both. I would definitely recommend ensuring properly airflow and then going back to have the system properly charged per subcooling. Without the proper airflow, you aren't getting full capacity or efficiency. A 3.5 ton system doesn't necessarily need 1400 cfm, but I would at least aim for 1225 CFM (350 cfm/ton). Your furnace should have a blower chart showing the airflow provided at various external static pressures. Since it's a standard, non variable-speed blower, it probably has a maximum static of 0.5" or less, which you may be over already.
    Thanks. The amount of returns does sound low to me. Whenever the system is on, the air going through the returns is pretty loud. We had the same problem with our old upstairs furnace, it also was short on return. Since we upgraded to a variable speed furnace upstairs, a new 10 inch return was added and now the cfm is balanced and everything is satisfied with that system.

  15. #75
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Quote Originally Posted by 545GAlady View Post
    Thanks. The amount of returns does sound low to me. Whenever the system is on, the air going through the returns is pretty loud. We had the same problem with our old upstairs furnace, it also was short on return. Since we upgraded to a variable speed furnace upstairs, a new 10 inch return was added and now the cfm is balanced and everything is satisfied with that system.
    Variable speed blowers are able to maintain proper airflow up to 0.8-1.0" static pressure, although I personally prefer to have the ductwork sized such that the static does not exceed 0.6" in residential. It was likely smart and necessary to add the additional return. Loud returns are symptomatic of high-velocity, high-static duct conditions.

  16. #76
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by RyanHughes View Post
    Variable speed blowers are able to maintain proper airflow up to 0.8-1.0" static pressure, although I personally prefer to have the ductwork sized such that the static does not exceed 0.6" in residential. It was likely smart and necessary to add the additional return. Loud returns are symptomatic of high-velocity, high-static duct conditions.
    Before our new upstairs furnace was installed, the contractor inspected all of the ductwork to see if it was sized properly. It turned out that all we needed was a new return. Our upstairs system is smaller than our main level system. Thanks for the input about loud returns.

  17. #77
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    All 7 returns are noisy, but the supplies are not.

  18. #78
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    I have no idea where the tech would actually put a new return.

  19. #79
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Might be able to increase the sizes of the existing return grills and duct

  20. #80
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by crmont View Post
    I hate to agree with Ryan but after looking at the pictures a little closer, it appears that there is a 16x20x1 air filter in place and it might even be an "allergy free" type filter. The return duct is also cut in one side of the furnace which historically makes for low airflow. Also the indoor coil looks suspiciously small for a 15 seer 3.5 ton. Please post the model numbers of the indoor coil and the Lennox furnace so i can verify the match up. Finally, have the static pressure checked and compared to the blower data. If the blower data isn't available, the furnace model number will clarify. Thanks.
    + another one for airflow problem.

    3.5 ton just for downstairs? How big is this house?

    Round hole? Not even using 16x20 at filter? Should we start making guesses what the ESP will come back at? How many think >1?

    You might want them taking ESP on upstairs unit while they are at it. ecm's tend to burn up when "driven around with the emergency brake on" (high static). Also, when techs test stuff, get the numbers they take and keep them in a file. Keeping these numbers is like tracking cholesterol levels, helpful to track over time, and sometimes useful for holding folks accountable. Just letting them know you'll want those numbers may bring out their A game.

Page 4 of 6 FirstFirst 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •