Page 2 of 9 FirstFirst 123456789 LastLast
Results 14 to 26 of 115
    Quote Originally Posted by 545GAlady View Post
    I already mentioned the indoor coil model number in one of my previous posts. Here it is again:
    4TXCBO42BC3HCBA
    That is an appropriate coil for the outdoor unit you have, so the equipment selection isn't the problem.
    Attachment 311391
    Model number is YTH9421C1002
    Honeywell VisionPRO IAQ
    Everything is compatible, it could just be the programing in the Tstat is not set up correctly allowing the furnace and HP to run simultaneously.
    Sep 2012
    The installers did test the emergency heat and the furnace itself did run in heat mode at that time. The heat pump lock out temperature is set at 40*F so the furnace will only run if it's below that temp outside. So I believe that part is set up properly.
    Sep 2012
    The furnace did not run at the same time as the heat pump. Only the blower was operating at the time besides the outdoor unit.
    Sep 2012
    Missouri
    Oct 2005
    Pacific Northwest
    Have the tech check the test mode jumper on the defrost board.
    Sep 2012
    Quote Originally Posted by crmont View Post
    OK I will. Thanks
    Sep 2012
    Is there a possibility that the unit is overcharged?
    Oct 2005
    Pacific Northwest
    Anything is possible, but a high or low pressure event usually doesn't reset in a few seconds as you described.
    JES
    Sep 2012
    Thanks. When the unit turned off, it was only off for about 10 to 15 seconds before it turned back on. Mostly 10 seconds.
    It is really bad for the compressor to attempt to start so quickly after shutting off.
    Sep 2012
    Yeah I thought so.
