Problem with Trane XR15
I had a 3.5 ton Trane XR15 heat pump installed last April. The unit replaced a 2002 Lennox 3.5 ton air conditioner (don't know the exact model number). The HVAC company did do a proper load calculation and said we were fine with 3.5 tons. The unit has performed flawlessly in COOL mode, but it seems to perform kinda weird in HEAT mode.
The unit heats and cools the main level of my house, and the main level is about 2200 sq ft. It is matched up with a 2002 Lennox G40 90,000 BTU input gas furnace with a 4 ton blower. So, the whole system is a dual fuel system.
I turned the heat on this morning and while it was running the heat pump outside turned off for a few seconds then turned back on. Then about a minute later it did the exact same thing. The blower stayed on the whole time and the thermostat still said "heat on". After a few minutes the heat pump turned off again for a few seconds and then back on, and it kept doing it repeatedly until the heat cycle ended.
Could this lead to anything bigger in the future? Is there something wrong with the unit? The unit doesn't do this at all in cooling mode.
Thanks
-
09-24-2012, 04:32 PM #2
Professional Member*
- Join Date
- Aug 2012
- Location
- willowick ,oh
- Posts
- 167
You need a service tech. ASAP. The heat pump is cycling off of high pressure switch. Ensure they add the dual fuel kit or fix their wiring. Trust me
-
09-24-2012, 05:00 PM #3
Call for service, could damage equipment
-
09-24-2012, 06:44 PM #4
Regular Guest
- Join Date
- Sep 2012
- Location
- GA
- Posts
- 306
Thanks. I forgot to mention that we are having our yearly fall tune-up done next Monday, and we probably won't need the heat within the next several days. So I might just mention it to the tech when he comes.
-
09-24-2012, 06:51 PM #5
Did they replace the indoor coil too?
If the indoor coil has a cooling only TXV, it won't allow proper refrigerant flow in the heating mode.If more government is the answer, then it's a really stupid question.
-
09-24-2012, 07:10 PM #6
Regular Guest
- Join Date
- Sep 2012
- Location
- GA
- Posts
- 306
-
09-24-2012, 07:16 PM #7
-
09-24-2012, 07:32 PM #8
Regular Guest
- Join Date
- Sep 2012
- Location
- GA
- Posts
- 306
-
09-24-2012, 07:42 PM #9
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,272
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
09-24-2012, 07:53 PM #10
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
09-24-2012, 08:03 PM #11
Regular Guest
- Join Date
- Sep 2012
- Location
- GA
- Posts
- 306
-
09-24-2012, 08:25 PM #12
What is the model number of the indoor coil, green box on top of the furnace, has copper and PVC pipes going to it.
If more government is the answer, then it's a really stupid question.
-