    Quote Originally Posted by cjpwalker View Post

    Skipping defrost coupled with strange fan behavior sounds more like a defrost terminator/fan delay switch problem to me. The epoxy seal on those breaks down over time and they fill with water.
    Yea I've witnessed very odd voltages when water gets in switches. You will get like 98 volts or 66 or somewhere inbetween , and the fan runs slow

    and like said above .... the case might just shock the hell outta you

  2. #28
    Join Date
    Dec 2008
    Location
    Nor•Cal
    Posts
    221
    Yup, any time I see an iced evaporator, first thing I do is mark the clock. Then continue with preliminary inspection and gathering model/serial info.

    I've definitely seen dtfd's cause the defrost timer issue as previously described. It terminates the instant it starts, so to speak.

    But, for what it's worth, I've seen fan behavior just like this which was caused by residual ice in the core of the evaporator, which blocked air flow through the coil and so the only other place for the air to travel through was through the "weaker" fan, fighting against it. (Note that weaker doesn't necessarily mean a defective fan, but in this scenario, one of them will dominate the other.) Pull the blade assembly off of the slower fan and see if the motor comes up to speed. And get a -bright- lite and make sure that coil is clear all the way through.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event