    York 80% furnace inducer motor

    York 80% furnace inducer motor starts right when gas fires? Shouldnt it run 10 seconds or so before gas fires?

    Sent from my SPH-D710 using Tapatalk 2

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,803
    It should be running long before the burners ignite. Get it checked before using it again.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Apr 2012
    Location
    chicago burbs
    Posts
    75
    Thats what im thinking, had a tech tell me this unit doesnt come on before burners. Its older, maybe the diamond 80. I just had to replace the inducer motor with the other tech and questioned why it didnt run before igniting.

    Sent from my SPH-D710 using Tapatalk 2

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,783
    That's not right. It should have to prove the inducer is running before igniting

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,803
    Its unsafe the way its operating. You need a good tech that knows what he is doing.