    York 80% furnace inducer motor

    York 80% furnace inducer motor starts right when gas fires? Shouldnt it run 10 seconds or so before gas fires?

    Sent from my SPH-D710 using Tapatalk 2

  2. #2
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,223
    It should be running long before the burners ignite. Get it checked before using it again.
    Contractor locator map

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Apr 2012
    Posts
    47
    Thats what im thinking, had a tech tell me this unit doesnt come on before burners. Its older, maybe the diamond 80. I just had to replace the inducer motor with the other tech and questioned why it didnt run before igniting.

    Sent from my SPH-D710 using Tapatalk 2

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson SC
    Posts
    2,467
    That's not right. It should have to prove the inducer is running before igniting

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,223
    Its unsafe the way its operating. You need a good tech that knows what he is doing.