    I PUT NEW EXV, BOARD, AND WIRE .I WIRED SAME COLOR CODE AS OLD EXV .I HAD NO INFO FOR NEW BOARD WIRING J4 1-5 AND J5 1-5 EXV WIRES BLACK WHITE RED AND GREEN
    tidewater, va
    will pull my notes out and see if i have anything on this as soon as i get ahold of the right book, I remember this issue
    Dec 2008
    Dixiana, AL
    Quote Originally Posted by clm7467 View Post
    Is there a question in there somewhere? And turn off the caplock - nobody likes someone that yells............
    tidewater, va
    Cant find any notes on this but will be out on a jobsite that i had this issue on this week and will check the wiring on it
    ottawa canada
    Dont think he heard ya Klove .... You may have to yell !!!!
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!
    Jan 2011
    Thanks for the help. I got the info for trane this morring .
    Southern California
    I am surprise that the new EXV's and board did not come with instruction or directions. I have the info.....6 years with factory Trane tech. next time don't CAP!!!!!
    Nov 2011
    South Texas
    Would you mind posting the new exv update instructions as a fyi. If not would you mind emailing them to me so I can through them in my memory banks if I have to do this on a few RTAA's under my supervision. Thanks
    tidewater, va
    believe the new exvs are SEHI valves and the wiring should be as on p.70 of RLC-SVD03A-EN. EXV #1 wired Red to J4-5 Green to J4-4 white to J4-2 black to J4-1
    EXV #2 red to J5-6, green to J5-5 white to J5-2 black to J5-1
    I made a copy of this page and put it with the wiring diagram when upgraded to the SEHI from the SEO valves
    Nov 2011
    South Texas
    Thanks a bunch good to have this
    tidewater, va
    page 70
    Attached Files Attached Files
    Feb 2013
    helps a lot to have the crimping tool and some extra plugs