correct layout of refrigeration piping in walk-in freezer
Good evening to everyone.
Most of the time I see that in walk-in freezers, the suction and liquid lines connected to the evaporator go immediately up and through the ceiling panel, exiting the walk-in as soon as possible. Is it correct to run the same lines across the walk-in and then though the wall panel? Does the low temp (-20F) may have some effect on the pipe insulation and/or the liquid refrigerant going through the liquid line?
Thank you for any responses.
-
09-22-2012, 05:05 PM #2
Just make sure the suction line is insulated properly, glue the ends of the armaflex to each other, secure it to the box, and make it look nice
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
09-22-2012, 05:11 PM #3
All of mine do just a you say. What wall thickness do you guys typically use on both medium and low temp applications? I've had so much trouble with condensation from the installer using 1/2" wall thickness.
-
09-22-2012, 05:55 PM #4
Professional Member
- Join Date
- Dec 2004
- Posts
- 484
-
09-24-2012, 08:02 AM #5
-
09-26-2012, 01:35 AM #6
Regular Guest
- Join Date
- Sep 2012
- Posts
- 9
One more thought about the piping being installed through the inside of the walk-in: the supports and hangers for the pipes most likely would have bolts going all the way through the walls and ceiling, with the possibility of condensation once these bolts get to the outside. Do you know of any design or type of support/hanger that minimizes this problem?
-
09-26-2012, 07:52 AM #7
What do mean? Are you talking about using all thread to go thru the ceiling and using pipe hangars? I like mounting uni-strut with pipe hangars. Depending on what's going in there you would be flirting with danger of having everything being eaten by acid. I would use all stainless steel hardware.
-
09-26-2012, 09:03 AM #8
Some installation specs call for nylon threaded bolts or rod like this:
http://www.usplastic.com/catalog/ite...4519&catid=668
I have used it, but have found the nylon easy to work with but it's easy to strip the threads if you're not careful.
Refrigeration Hardware has some fiberglass reinforced rod which works quite well and is a lot stronger (See p.125):
http://www.rhsparts.com/pdf/2007GENP...ag%20Bolts.pdf