    gas pressure 7.0 before valve 3.5 after valve flames are rolling out & into burners burners are clean,cleaned pilot,new thermocouple w/ cleaning chimney is clear!What else can make this roll out into the burners?
    Virginia
    Quote Originally Posted by heat411 View Post
    Here are some of the other things I would be looking for -
    Improper Venting.
    Inadequate Combustion Air Supply.
    Incorrect/Plugged Burner Orfices.
    Bad Inducer Motor and/or Motor Capacitor.
    Sooted Heat Exchanger.
    Bad Heat Exchanger.
    Jul 2009
    Columbia, MD
    because its a goodman!
    make sure your runners are clean, orifices arent clogged, and inducer motor and inducer wheel are clean.
    what type of furnace? what type of ignition system?
    Jan 2002
    Palatine Il.
    Has the gas valve been replaced. If so It might have the wrong type of valve. It may need a slow opening valve, but a fast opening was installed, as an example.
    Hi, my name is Glenn, and I'm a Toolaholic!
    Calgary, Alberta
    There are certain natural draft appliances which will roll out if the burners are not exactly lined up and inserted ALL the way.
    Did you run the appliance before you did this work to see if it was doing this before you got there?
    Nov 2001
    Moose Jaw, Saskatchewan, Canada Occupation:Interprovincial Plumber, Commercial Gasfitter Interests:
    What type of boiler? If it is a fin-tube, you have to make sure the fins are clean.
    I love my job, but paydays Thursday
    Jan 2010
    Toronto,Ontario Canada
    things i would check.
    1. the pilot might not be sitting in properly. make sure its in the way of the pilot asembly. watch it while it lights its self. if it takes too long then adjust your pilot.
    2. If it is a standing pilot-make sure the pilot tubing isnt leaking at the assemble (base) Test-check the pilot when its not calling at the assembly *most likely the cause*
    3. quick opening or slow opening will do it. if u matched it up then u should be fine.
    4. clean the pilot tubing with vinegar i was told it cleans it well and it works for me a few times
    5. make sure you can see thru the heat exchanger with a flashlight you may have a blocked heat xchanger.
    6.i havent mentioned this but its a good idea to check the condition of the burners any cracks oh ya. make sure the burner is in the right place for the ignition i have done it where i had it go on the one side where it should have gone somewhere else. when i take out burners i usually label the manifold with a black X
    Hope that helps.
    Good luck
    Get er Done!
    Do what has to be done
    when it has to be done
    as well as it has to be done
    And doing it all the time.
    Jul 2009
    Columbia, MD
    do u think he blew up?
    Jan 2010
    hope not. oh well the customer doesnt need heat at this time its safe to leave it off fo now til someone else goes back there.
    Get er Done!
    Aug 2012
    west burbs,il
    Lmfao!!
    Jan 2015
    Bellevue, Washington, United States
    Might be a gas valve opening too quickly. more likely your exchanger is clogged with soot
    north suburbs of Chicago
    Might be Youtube Rolland at his neighbors home now after he fixed his own unit.
    If flames are rolling out even after ignition about all you can have is a plugged boiler if it's not a power vent/inducer. Chimney plugged on nat draft would spill at the hood. If flames are burning inside the burners that's usually air/fuel problems or ignition. You said you had flame rollout plus burning inside the venturis?