The hvac contractor that quoted the job has actually seen the drawings/building and designed the system. No one on this site has so it is only speculation, sounds like what the contractor is on the right track and is going to satisfy your needs. Applications such as yours are NOT cheap endeavors so a 5 figure number does not sound out of line.
-
09-23-2012, 10:11 PM #17
Professional Member*
- Join Date
- Feb 2006
- Location
- Atlanta,GA.
- Posts
- 732
sounds like refrigeration units for warehouse which would be normal,but because it is split into several units if one goes down you would at least maintain some cooling in the area. hopefully the contractor ran heatload calc on space, the insulation in warehouse area seems a little light to me dont know why they arent using insulated cooler walls because you will need to be tight in the cooler area otherwise you will have moisture problems in walls
-
10-02-2012, 04:40 AM #18
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,355
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-02-2012, 04:59 AM #19
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,355
http://www.trane.com/COMMERCIAL/DNA/View.aspx?i=1062
http://www.trane.com/download/equipm...RC007EN_r2.pdf
At first glance, one 20 ton unit seems to be MORE THAN sufficent for both the Production and retail space.
I believe that cooling in each area is << 10 tons.
DX based equipment is frequently Going in the Wrong direction for industrial applications.
If one ACTUALLY Neeeds < 72'F room temperature, a very small chiller and a few air handlers will meet requirements.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-02-2012, 05:47 AM #20
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,355
Small chiller, 20 ton, Page 41
http://www.trane.com/download/equipm...RC007EN_r2.pdf
Figure DD-3 — CGAF-C20 Unit Dimensions
or 15 Ton might be the needed capacity, page 40.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-02-2012, 06:09 AM #21
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,355
I might not have to much problem deciding on
_________ Who's recommendation to follow ?
___________ Your G.C. or my 3 year old grandson.
Example...
Perimeter = 75 +50 +50 = 175 feet
A = 175 * 15' height = 2,625 sq feet; roughly 3,000
Q wall production area = A * dt / R = 3,000 * 30 / 20 = 4,500 BTU/hr
... minimize condensation issues .:. Supply Air at ~ 50'F with 8 or 10-row coil.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities