    Using old tubing with new 410a equipment

    What are the results of using old tubing from an R-22 system that is being converted to 410A? I have been able to use new tubing until now, where it is very impractical. Supposedly you can flush the existing tubing to remove the mineral oil. What have been the results in the real world?

  2. #2
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    unless theres somehow an excessive amount of oil in the lines, you don't need to do anything different than you would if swapping out R-22 equipment. mixing the oils doesn't create some sort of super sludge like the flush companies want you to believe.

  3. #3
    Join Date
    Sep 2012
    Location
    Harrisburg, PA
    Posts
    12
    Post Likes
    Make sure you confirm the size of the line set!!! also make sure you use the flush.

  4. #4
    Join Date
    Mar 2007
    Location
    AR
    Posts
    2,489
    Post Likes
    I worry more about the flushing agent than I do the oil so I dont flush unless its a burn out.

  5. #5
    Join Date
    Sep 2012
    Location
    Port Aransas, Texas
    Posts
    71
    Post Likes
    Thread Starter
    Experience counts. You guys feel like this is a concensus everywhere? If your experience and that of your peers tells you that there are more imprtant things to worry about, then I won't get too concerned about it. They said a lot of things about 410A in the beginning. I like this one: Do not charge vapor. Do not top off. Then they report that testing has shown that a leaking system can be topped off something like 35 times with no noticeable effect. Love the internet.

  6. #6
    Join Date
    May 2011
    Location
    Pennsylvania, USA
    Posts
    48
    Post Likes
    Just verify the line sizes are correct for the new equiptment. Do a tripple evacuation.

  7. #7
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Don't forget to change FD.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Make sure line set size is ok. Then blow it out with nitro.

    Its still best to only charge r410a as liquid only.

    The false rumor you heard about not topping off was from sourves that either didn,t have any training on it, or were just prejuctice against it.

  9. #9
    Join Date
    Nov 2011
    Location
    Phoenix,AZ
    Posts
    466
    Post Likes
    nearly all the linesets here are behind drywall so replacing them is not an option not to mention most people wont pay extra for them to be replaced.

  10. #10
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    I just blow with nitro and pull a good vac with a micron gauge. When we first started installing 410 we used the flush but I feel like it will do more harm than a little oil. That flush is some potent stuff, smells like nail polish remover and burns your eyes. Trane install manual says to NOT use ac flush

  11. #11
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,420
    Post Likes
    how would trane know.... lol
    it was working.... played with it.... now its broke.... whats the going hourly rate for HVAC repair

  12. #12
    Join Date
    Feb 2007
    Location
    joliet il.
    Posts
    14
    Post Likes
    I would make sure there are no soft solder joints in it first!Back in the day , alot of installers used 50/50 or 95/5 on there joints! 410a pressures may cause a failure at this type of joint! Nitro flush is is a minimum prep.

  13. #13
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by Mark s View Post
    I would make sure there are no soft solder joints in it first!Back in the day , alot of installers used 50/50 or 95/5 on there joints! 410a pressures may cause a failure at this type of joint! Nitro flush is is a minimum prep.
    A 3/8 line with 400 psi inside is experiencing about 17 pounds of force pushing the connection apart. Bubble gum would almost be capable of holding that together.

  14. #14
    Join Date
    Feb 2007
    Location
    joliet il.
    Posts
    14
    Post Likes
    http://www.descoenergy.com/pdf/York%...ZE%20R-410.pdf Bottom of page 2,, line brazing, Do Not Soft solder!!

  15. #15
    Join Date
    Sep 2012
    Location
    Port Aransas, Texas
    Posts
    71
    Post Likes
    Thread Starter

    Say what?

    Quote Originally Posted by craig1 View Post
    A 3/8 line with 400 psi inside is experiencing about 17 pounds of force pushing the connection apart. Bubble gum would almost be capable of holding that together.
    Craig1 -- You lost me, dude.

  16. #16
    Join Date
    Feb 2007
    Location
    joliet il.
    Posts
    14
    Post Likes
    Is that Sugarless gum?? HAHA

  17. #17
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by mustanger361 View Post
    Craig1 -- You lost me, dude.
    pressure is measured in PSI, Pounds per Square Inch. If you had two 1 inch square pieces of tubing and joined them together and charged them with 400 PSI there would be 400 pounds of force pushing them apart.

    However, the inside of our liquid line is not 1 square inch, it is a small portion of that.

    the inside diamer of 3/8 tubing is 1/4"

    the area of that inner diameter is .049 square inches.

    multiply that times 400 and you get 19.6 pounds of force pushing the joint apart.

  18. #18
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by Mark s View Post
    Is that Sugarless gum?? HAHA
    Sugarless is recommended for 410a. It has a higher tensile strength. Thats why you can blow bigger bubbles if you chew gum long enough to get all the sugar out.

  19. #19
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by craig1 View Post
    pressure is measured in PSI, Pounds per Square Inch. If you had two 1 inch square pieces of tubing and joined them together and charged them with 400 PSI there would be 400 pounds of force pushing them apart.

    However, the inside of our liquid line is not 1 square inch, it is a small portion of that.

    the inside diamer of 3/8 tubing is 1/4"

    the area of that inner diameter is .049 square inches.

    multiply that times 400 and you get 19.6 pounds of force pushing the joint apart.
    I come up with .2956 sq in surface area, which would be a total of 117.8 pounds of force.

  20. #20
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by beenthere View Post
    I come up with .2956 sq in surface area
    I don't guarantee my calculation is correct, but I do guarantee yours is not

    Theres no way a 1/4" circle takes up more than 1/4 of the area inside a 1"x1" box


+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •