    Installed a 95 percent goodman gas hot air furnace with a 3 ton air cond system in a prebuilt home. Air cond worked like a charm but when the furnace is on the roll out switches kick out with no apparent rollout visiable. Bad rollout switches? Any ideas on what is going on. First goodman I have installed
    Jul 2010
    nebraska
    I'd suggest rereading the venting instructions and starting there.
    Aug 2001
    Pavilion, NY
    What is the gas pressure, temp rise, carbon monoxide and carbon dioxide in the vent?
    Urbandale IA. USA
    Low air flow to the home can cause roll outs to trip.
    Check the flue for blockage. You could have a wasp nest or other obstruction that is NOT causing pressure sw problems, but flue gas temps will rise.
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.
    Jan 2011
    Cincinnati Ohio
    Was it installed as a two pipe system? As stated previously check the venting for obstructions. Also check the gas pressure.
    Sent from my Nexus 7 using Tapatalk 2
    Oct 2011
    between here and over there
    did you check out the orifice in the manifold? I once installed a furnace with natural gas orifice in them, didnt take notice that there was a propane tank around the house, neither did the sales man... later that season there was a call back.. guess what for..
    May 2012
    Upper Michigan
    Quote Originally Posted by Trehak01 View Post
    Did that too.
    Aug 2012
    MN
    I got sent back to a new install that would run for about 5 minutes then open roll out. It had an auxillary limit with the same rating so I switched them with the same result. Gas pressure was good, orfices correct, venting clear, but co super high. Ended up being to much oil left in secondary at factory.
    burlington county n.j.
    MJG and pcp
    Additional infractions may result in loss of posting privileges.
    scroll up........... this is tech to tech......
    Aug 2012
    MN
    If home owners are asking these questions I hope no one responds.
    Quote Originally Posted by t527ed View Post
    Oops.
    I fixed the posts.
    Quote Originally Posted by pcp View Post
    Stick around. Not all of the mods are idiots, just me.
    You'll find a LOT of homeowners ask similar questions.
    Oops.
    I fixed the posts.
    Its because you were wishing you were at CT with the rest of us. That you forgot that you moved this to Tech to Tech. LOL