  1. #21
    Join Date
    Feb 2005
    Location
    Alabama
    Posts
    530
    Post Likes
    I couldn't agree more alpha.
    "If you can't fix it, don't break it."

  2. #22
    Join Date
    Mar 2006
    Location
    Middle Tennessee
    Posts
    110
    Post Likes
    I've only used the Yellow Jacket SuperEvacIII and it worked flawlessly.

    After following several threads here it was aparent that nobody upgrades to something better after they use the 60975, although some have had trouble with the core removing valves.

  3. #23
    Join Date
    Sep 2004
    Location
    Nova Scotia, Canada
    Posts
    153
    Post Likes
    Guys, Guys, This is a state-of-the-art micron gauge which is attached to my old Welch Duo-Seal 2-Stage belt driven vacuum pump (Model 1400). It can still pull down to about 800-900 microns. Only problem is it needs a new shaft seal


  4. #24
    Join Date
    Jan 2005
    Location
    Veterans Home Yaphank, NY
    Posts
    2,309
    Post Likes
    Quote Originally Posted by ;1256224
    Since we're on the topic of vacuum, I have a question. First off I pull a vacuum whenever I have to open a system, I also use a micron guage. I've been getting conflicting statements on "how" to pull the vacuum. Some say pull from one side only i.e the vapor line, others say pull from both sides at the same time. Which is correct, or does it matter? I take pride in my work and always want to learn more. Thanks, Bill
    Install hoses from manifold on both high side and low side, 3/8" line to vac. pump, 4th line to refrigerant tank. tee on vaccuum pump for micron gauge.
    Open high side handle on gauge manifold, vacuum pump handle, start pump.
    Observe low side gauge to see if it goes into vacuum, if it does continue to pull down to 15" hg, then open high side handwheel. If you do not see low side going into vacuum, then you have a restriction. Continue evacuation to 500 microns(250 on Manitowac Ice machines),close hand wheels on manifold and observe micron gauge. Rapid rise=leak, slow rise=moisture. No rise after 15 minutes= URgood
    RAM Teaching Tomorrows Technicians Today.

  5. #25
    Join Date
    Jan 2006
    Location
    Hangin out with you losers
    Posts
    1,043
    Post Likes

    Thumbs up

    Quote Originally Posted by ;1256302
    Either way will achieve the same effect, but the time it takes to do that will vary.

    The best way is to pull from both sides, hooking the micron gauge up to the farthest point from the vac pump (which would be the coil in almost all cases).

    Now, you could hook one hose to one side of the system, your micron gauge to the other side of the system aswell... but that'll take a long long time.

    Or, you could do what most people do... using a 4 port gauge system, hook 2 hoses to the unit, one for the micron gauge, and one to the pump. Shut the pump one down and let it sit. If it goes up past 500, you need to keep going (or fix your leaky hoses). Not the 100% accurate way, but it's (in this writers opinion) plenty good enough for all but very very touchy systems.
    This is the method that I use
    And I will have to say has made me a ton of money
    I find more leaky evaps this way then any other.
    If I cant get 500 there is a leak and I find it
    I remember my first day,It was fun!

  6. #26
    Join Date
    Oct 2004
    Posts
    1,722
    Post Likes
    I use the same setup that Mark does. With the ball valve at the sensor and stainless hoses.

    Mark, without the ball valve between the sensor (in the picture), did you still open the valves or add refrigerant to the system with the sensor on the port?

    I also have the same problem with the o-ring in one of their core tools. Looks like it's been chewed. I'll have to replace it before I use it again. Have you had better luck with C&D?
    Get back to work.™

  7. #27
    Join Date
    Oct 2001
    Location
    Stoney Creek, Ontario
    Posts
    885
    Post Likes
    every one seems to use a micron guage. i would guess that 90 % of resi contractors do not use one

    i dont do resi, but that is what i have seen

  8. #28
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by square2round View Post
    I use the same setup that Mark does. With the ball valve at the sensor and stainless hoses.

    Mark, without the ball valve between the sensor (in the picture), did you still open the valves or add refrigerant to the system with the sensor on the port?

    I also have the same problem with the o-ring in one of their core tools. Looks like it's been chewed. I'll have to replace it before I use it again. Have you had better luck with C&D?
    Before I put a ball valve in to blank off the sensor from the system I would break the vacuum to just a few psig with refrigerant, then remove the sensor and continue charging. I didn't go for very long without the ball valve though.
    Having the ball valve on it allows me to just start dumping refrigerant in without having to worry about the sensor.

    The C&D core removers have a double o-ring seal and a brass flare that seats against the service port. The o-rings die quickly, but the flare makes a really good seal if you put a little Nylog on it.
    One of these days I'm gona order 1 of each brand of core removers and find out who makes the best ones.
    So far I have only used the Yellow jacket ones, which suck, the C&D ones with a gate valve, which also suck, and the C&D ones with the ball valve, which work very well if you throw the o-rings away and put a little dab of Nylog on the flare every 2nd or 3rd time you use them.

  9. #29
    Join Date
    Mar 2006
    Location
    DFW
    Posts
    3,967
    Post Likes
    NOT using a micron gauge is like trying to measure 2" using your cars odometer.
    Eat a slice of Humble Pie.

  10. #30
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    I got a friend of mine good a few months ago. He was one of those techs that thought the evacuation was done when the pump didn't sound different when you closed the valve, and would argue passionatly about it.

    I hooked up my vacuum gauge to a system he was working on, he had already decided the evacuation was done because his pump didn't change sounds when he closed the valve. The reading was around 10k microns. It wouldn't go any lower though, so we tried seeing how low his pump would pull just the gauge, it wouldn't go below 10k microns, even with an oil change.
    I grabbed my pump and it pulled the gauge down to 40 microns, so we finished the evacuation down to 400 microns with my pump.

    About 2 days later he bought a new pump and micron gauge. Just a cheep little colored LED light one, but its a start. I used one of those for years before I got my Yellow Jacket one, and it still actually works fairly accurately after 10ish years.

  11. #31
    Join Date
    Nov 2006
    Location
    The Heart of It All
    Posts
    303
    Post Likes
    ditto what most have already said,i love micron gauges be cause nothing will show you any faster that there is a leak if you have one,no matter how small the leak.i use the 500 + 250 rule, vac to 500,if it doesnt rise above 750 after 35 t0 40 min,gas n go baby

  12. #32
    Join Date
    Aug 2002
    Location
    Louisville
    Posts
    283
    Post Likes
    Look at the chart it will give you the obvious reason to evacuate. Especially in a heat pump, Ice-machine, and low temp refrig. That being said look at the boiling point of water at a 29" vacuum. With the refrigerant temp in the evap of a residential ac unit ,which is more forgiving than the previously mentioned systems, at 40 degrees design do you see what will happen ? HYDROCHLORIC ACID and Hydroflouric Acid. Look at the common denominator Hydro. Remove the hydro through evacuation and you remove future damage.

  13. #33
    Join Date
    Oct 2004
    Posts
    1,722
    Post Likes
    Quote Originally Posted by mark beiser View Post
    Before I put a ball valve in to blank off the sensor from the system I would break the vacuum to just a few psig with refrigerant, then remove the sensor and continue charging. I didn't go for very long without the ball valve though.
    Having the ball valve on it allows me to just start dumping refrigerant in without having to worry about the sensor.

    The C&D core removers have a double o-ring seal and a brass flare that seats against the service port. The o-rings die quickly, but the flare makes a really good seal if you put a little Nylog on it.
    One of these days I'm gona order 1 of each brand of core removers and find out who makes the best ones.
    So far I have only used the Yellow jacket ones, which suck, the C&D ones with a gate valve, which also suck, and the C&D ones with the ball valve, which work very well if you throw the o-rings away and put a little dab of Nylog on the flare every 2nd or 3rd time you use them.
    I was very hesitant to put any pressure on the sensor. Although it sounds as if a few psig didn't hurt it.

    I've got to look into another core remover also. There's gotta be something better.
    Get back to work.™

  14. #34
    Join Date
    Jan 2007
    Posts
    1,360
    Post Likes
    you came to the right place if you want to learn about pulling it..... and vacuum's.... we be experts at that stuff.

  15. #35
    Join Date
    Dec 2005
    Location
    Sooner Nation!
    Posts
    103
    Post Likes
    I do a lot of "res", ALWAYS use micron gauge. To me is is INSURANCE against call backs.
    "Democracy--Two wolves and a sheep voting on what the menu is for lunch.
    Liberty--Is a well armed sheep who will probably contest the vote." author unknown--but I like him already

  16. #36
    Join Date
    Aug 2006
    Posts
    442
    Post Likes
    Pulling a vacuum with a micron gauge is a most. I bought the new Yellow jacket with the thermocouple. Best investment I have made in while. I micron gauge everything that my vacuum pump touches. Hook the gauge up to the system or inline with the hoses. If you hook up on top of the pump then you are reading the vacuum pumps capacity not the level in the system

  17. #37
    Join Date
    Jan 2006
    Location
    Hangin out with you losers
    Posts
    1,043
    Post Likes
    Quote Originally Posted by hvaccop View Post
    Pulling a vacuum with a micron gauge is a most. I bought the new Yellow jacket with the thermocouple. Best investment I have made in while. I micron gauge everything that my vacuum pump touches. Hook the gauge up to the system or inline with the hoses. If you hook up on top of the pump then you are reading the vacuum pumps capacity not the level in the system
    Agree!

    Everything I was ever told or read says place the micron gauge as far away from the vacum as possible
    The best possible place is the evap I hear.
    I dont do that
    I use a 4 way gauge
    3/8 to vac
    1/4 to each service conection
    and 1/4 to micron gauge
    I dont trust my vacums ball valve ever
    I remember my first day,It was fun!

  18. #38
    Join Date
    Jul 2006
    Location
    tri state
    Posts
    296
    Post Likes
    I have always pulled from both sides and finished by pulling from suction port in the last few min. of vac.
    life is at its best when u learn something new.

  19. #39
    Join Date
    Apr 2002
    Location
    Wilkes-Barre/Scranton, PA
    Posts
    521
    Post Likes
    I have used a Thermal Engineering analog micron gauge for many years and just last year I bought a JB handheld digital and it seem so be a pretty good little unit. Anyone else have any opinions about the JB?

  20. #40
    Join Date
    Nov 2006
    Location
    Oregon
    Posts
    853
    Post Likes
    Quote Originally Posted by AirTechMech View Post
    I have used a Thermal Engineering analog micron gauge for many years and just last year I bought a JB handheld digital and it seem so be a pretty good little unit. Anyone else have any opinions about the JB?
    No but I sure have an opinion about the Thermal Eng 14571 analog gauge. I love it. It's accurate, easy to use and I really like to see the progress I'm making all the way from atmosphere down to the <500 micron level.

    I also have a Fieldpiece digital micron gauge and it's going on Ebay pretty soon. The two units match very closely but the Fieldpiece leaves me blind with what's happening until I'm below 2000 microns.

+ Reply to Thread
Page 2 of 9 FirstFirst 123456789 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •