    Old McCall refrigerator

    I'm trying to get correct cap tube size on this r-12 upright. Delfield said model number doesn't exist when i called!!! Here's a pic of the data plate. Can anyone help. Unit could have had a dual feed originally or even a txv w/ receiver.I don't know!!! It looks like Model# 6045 to me and Serial # M-21512.
    Thanks
    Attached Images Attached Images  

  2. #2
    Join Date
    Jul 2001
    Location
    Gold Coast of Connecticut
    Posts
    4,656

    supco

    Quote Originally Posted by KB Cool View Post
    I'm trying to get correct cap tube size on this r-12 upright. Delfield said model number doesn't exist when i called!!! Here's a pic of the data plate. Can anyone help. Unit could have had a dual feed originally or even a txv w/ receiver.I don't know!!! It looks like Model# 6045 to me and Serial # M-21512.
    Thanks
    http://www.supco.com/images/pdfs/Man...0Reference.pdf
    Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced

  3. #3
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,895
    Yeah, i did that already cut 78" of bc2 and got 13 oz of mp39 in it before i had to stop. Data plate says 32oz! WTF!!!!! Did this thing have a receiver originally?

  4. #4
    Join Date
    Jul 2001
    Location
    Gold Coast of Connecticut
    Posts
    4,656
    Quote Originally Posted by KB Cool View Post
    Yeah, i did that already cut 78" of bc2 and got 13 oz of mp39 in it before i had to stop. Data plate says 32oz! WTF!!!!! Did this thing have a receiver originally?
    It could have but if it was working well it does not matter. With a 1/3 HP comp what you did should get it running 170/20 and work fine
    Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced

  5. #5
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,565
    why did you have to stop?

    Was this a tecumseh AEA4440AXA? If so, you need to use the HIGH TEMP column of the Supco chart. You should have around 36" BC 2 and i usually chop it down to 28-30" if I can't attach it to the suction line for heat exchange.

  6. #6
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,895
    It's an ARE37C3-IAA-901


    I stopped because pressure looked like they were supposed too. Ambient 100 High side 240 lo 30. Low dropped to around 25 before i left. Box temp at 42. Liquid line was 116.
    Due to the High ambients. I want to put it back to factory and charge w/ r-12. It's in a snack bar at a outdoor amphitheater. Get's used maybe twice a month. I fixed their walk in and guy asked me to look at this upright. I made him no promises due to no A/c in building!! Can i get it to work?

  7. #7
    Join Date
    Dec 2000
    Location
    Flat Rock, NC
    Posts
    463
    That liqiud line temp looks way to high. Might try jb industries cap tube sizing chart. I never had good luck with such a short tube.

  8. #8
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,483
    Check out Tecumseh's cap tube selection application written by Andy Schoen: Tecumseh Capillary Tube Sizing

    I've used it many times with much better results than any of the old charts.

  9. #9
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,895
    Quote Originally Posted by icemeister View Post
    Check out Tecumseh's cap tube selection application written by Andy Schoen: Tecumseh Capillary Tube Sizing

    I've used it many times with much better results than any of the old charts.
    How do you use it. I'm not seeing any copeland's compressor's to choose from. And would i enter 130 for condensing temp? 45 evap? around 3600 btu at those conditions.??? What's the capacity at +20 sst? Compressor model # AREARE37C3-IAA-901
    Thanks

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,483
    Quote Originally Posted by KB Cool View Post
    How do you use it. I'm not seeing any copeland's compressor's to choose from. And would i enter 130 for condensing temp? 45 evap? around 3600 btu at those conditions.??? What's the capacity at +20 sst? Compressor model # AREARE37C3-IAA-901
    Thanks
    Now why would one expect to see Copeland ratings on a Tecumseh program?

    To use it, you have a choice of either selecting a Tecumseh compressor from the dropdown list or enter a capacity at the conditions you enter.

    You can use the Tecumseh Competitive Cross Reference program to find an equivalent Tecumseh compressor, which in this case would be an AEA4440YXA, and select that. Or you could simply look up the Copeland compressor's capacity on the Emerson website.

    For the Tube ID, you can either let the program Auto-Select the ID of cap tube for you or you can specify an ID from the dropdown list. If you specify an ID, you need to check what the resulting length is and try to stay with about 5 ft as a minimum and 12 ft as a maximum length and adjust the ID accordingly.

    For the operating conditions, it varies with the type of system you have and its manufacturer, but in general you can use +20F SST and 120F SCT for a typical reach-in cooler. That's based on an assumption of 20F below box temp and 30F above ambient. It'll get you pretty close.

    You also want to pay attention to the part about heat exchange length. This refers to the length of cap tube which is going to be attached to the suction line to act as a heat exchanger. It make a significant difference in the length of cap tube required.

    The default heat exchange length of 36" is fairly typical on most systems. Due to limitations built into the program, the minimum heat exchange length is set to 6", so if you're not attaching the cap to the suction, use 6" anyway.

  11. #11
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,895
    Thanks Icemeister. Seems like i'm way too long at 78" compared to the Tecumshe calc. Why wouldn't they be the same?? Maybe i'll go back and cut 30" off!!

  12. #12
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    471
    Is this a large unit with the evaporator on lefthand vertical wall, condensing unit on top? Could it be a converted pizza retarder? I've seen a few old R12 McCall pizza retarders. They all have TXV's. I just recently replaced the TXV in one, it's working very good using a pressure control switch for temperature control and R409A.

  13. #13
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,895
    Quote Originally Posted by Capz View Post
    Is this a large unit with the evaporator on lefthand vertical wall, condensing unit on top? Could it be a converted pizza retarder? I've seen a few old R12 McCall pizza retarders. They all have TXV's. I just recently replaced the TXV in one, it's working very good using a pressure control switch for temperature control and R409A.
    No, condensors on top. But evap is mounted to the ceiling in the center.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event