    Jan 2006
    Can someone explain to me a little better about Cool Gas defrost for racks? How it works step by step. Im running into more and more and I want to make sure I really have it down perfectly.
    Jan 2006
    Indiana
    Cool gas defrost systems use cool gas(vapor) from the top of the receiver instead of hot gas(discharge). The defrost valve, which is piped into the top of the receiver, energizes sending cool gas through the suction line to the cases. There is a bypass with a check valve around the txv. The refrigerant returns to the liquid header through liquid line. There is a solenoid in the main liquid header that closes on defrost with a pressure differential check valve,usually 20psi, piped in parralel. A pressure differnce is created by the closing of the solenoid which allows the returning refrigerant to flow into the liquid header. If the pressure drop increases above 20psi the check valve will modulate to allow enough liquid through to feed the remaining cases. If you have a solenoid for each circuit there will be a bypass for each of those also. If there is heat reclaim it should shut off during defrost to keep enough heat in the receiver for proper defrost.
    Jan 2006
    you the man
    Sunny So Cal!
    its Koolgas and search the archives-
    condenseddave has a tight explanation.
    Look, just do your job, stay outta my way and we'll get along fine.
    Teach your kids to respect themselves and others with your actions- these little baboons will imitate you like it or not.