    Relay position sensitive?

    We have installed 4 Trenton condensing units in the past several months. Each one has had the potential relay installed with the top arrow pointing down. Supply house tells us they are no longer position sensitive but are still labeled as such. I've turned them around none the less, but was wondering if that is the case?

  2. #2
    Join Date
    Apr 2009
    Posts
    128
    From my experience, if they have an arrow, they are position sensitive and I would instal them in the correct position. I changed one out that was burnt very recently. I didn't realize it was upside down. I was drawing 30 amps because the relay wasn't able to come out of start. Like I said, that's just my experience.


    Quote Originally Posted by DeluxeDave View Post
    We have installed 4 Trenton condensing units in the past several months. Each one has had the potential relay installed with the top arrow pointing down. Supply house tells us they are no longer position sensitive but are still labeled as such. I've turned them around none the less, but was wondering if that is the case?
    Max Igan- The Energetic Universe

    https://www.youtube.com/watch?v=4RclaITj8D4

  3. #3
    Join Date
    Apr 2007
    Location
    Scottsdale,AZ
    Posts
    78
    If it has an arrow I would position correctly.
    There are some that are not position sensitive.