Thread: New Carrier 3 ton, 16 SEER HVAC and air handler issues

  1. #1
    Join Date
    Jun 2012
    Posts
    23
    Post Likes

    Confused New Carrier 3 ton, 16 SEER HVAC and air handler issues

    Hey all...I was out here in June and early July investigating options for replacing my older Carrier, 3 ton, 13 SEER HVAC system (outside unit was very noisy and had a hard start added to it, but we felt we were on borrowed time)...Long story short, we went with installing a new air handler (same variable speed, etc) and a new outside unit (Carrier, 3 ton 16 SEER upgraded outside "cage")...When they installed the system, the old system didn't seem to have the appropriate "plenums", so they added new plenums (at no charge to me). Ever since we had this new system, electric bills were higher and we checked out our usage and it seemed to be in line with our usage the year before, so we didn't dwell on that at the time...Our issue is that although the thermostat states 72 (we set it there and never change it - set on cool)...It seems to be hotter than 72....Our remote control for our fireplace has a temp reading on it, so we moved it from room to room and it was pretty consistent with saying it was really 74-75 degrees in each room. We contacted the company that installed the unit and they came out to do their check up (post install checks and balances, I guess)...They found that there were a couple of places that were not sealed all that well on the air handler, so they rectified that, but didn't feel it would create the issues we felt we were dealing with. They started talking about humidity and that made sense...It was a humid 72 versus the 72 we were used to...At any rate, they tested the defrost board (not sure that is the right term) and decided that it needed to be replaced. Keep in mind, this is supposed to be a brand new unit right out of the box! We weren't happy that a part needed to be replaced right off the bat, but it wasn't costing us, so we accepted that as a potential fix.

    We still experienced the same issues over the next 30 days and had the company sales rep come back out. He used some commercial readers (sticks that read temp, humidity and some other stuff) and left them in two different rooms over a period of 10 or so days. They just sent us a copy of one of the data results and the temp only varied by 3 degrees, but the humidity varied considerably (up to 61.1% - varied a lot)...

    Does anyone have any suggestions as to what could be causing this new system to feel like it isn't doing as good of a job as my old failing 13 SEER Carrier system???JamesRiverAir_HVAC_MonitoringReport.pdf

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by CoastalWGSD View Post
    Hey all...I was out here in June and early July investigating options for replacing my older Carrier, 3 ton, 13 SEER HVAC system (outside unit was very noisy and had a hard start added to it, but we felt we were on borrowed time)...Long story short, we went with installing a new air handler (same variable speed, etc) and a new outside unit (Carrier, 3 ton 16 SEER upgraded outside "cage")...When they installed the system, the old system didn't seem to have the appropriate "plenums", so they added new plenums (at no charge to me). Ever since we had this new system, electric bills were higher and we checked out our usage and it seemed to be in line with our usage the year before, so we didn't dwell on that at the time...Our issue is that although the thermostat states 72 (we set it there and never change it - set on cool)...It seems to be hotter than 72....Our remote control for our fireplace has a temp reading on it, so we moved it from room to room and it was pretty consistent with saying it was really 74-75 degrees in each room. We contacted the company that installed the unit and they came out to do their check up (post install checks and balances, I guess)...They found that there were a couple of places that were not sealed all that well on the air handler, so they rectified that, but didn't feel it would create the issues we felt we were dealing with. They started talking about humidity and that made sense...It was a humid 72 versus the 72 we were used to...At any rate, they tested the defrost board (not sure that is the right term) and decided that it needed to be replaced. Keep in mind, this is supposed to be a brand new unit right out of the box! We weren't happy that a part needed to be replaced right off the bat, but it wasn't costing us, so we accepted that as a potential fix.

    We still experienced the same issues over the next 30 days and had the company sales rep come back out. He used some commercial readers (sticks that read temp, humidity and some other stuff) and left them in two different rooms over a period of 10 or so days. They just sent us a copy of one of the data results and the temp only varied by 3 degrees, but the humidity varied considerably (up to 61.1% - varied a lot)...

    Does anyone have any suggestions as to what could be causing this new system to feel like it isn't doing as good of a job as my old failing 13 SEER Carrier system???JamesRiverAir_HVAC_MonitoringReport.pdf
    Did they leave you any service tickets with technical data such as pressures and temperatures etc.?

    Rather unusual for the defrost board to be replaced when insufficient cooling is the problem. Is this in southern Va.?

  3. #3
    Join Date
    May 2012
    Location
    San Diego, CA
    Posts
    352
    Post Likes
    The general question that everyone asks is did you get a load calculation done? Humidity problems are usually due to oversized units. Higher electricity bills may also mean shorter on cycles because of oversized units. Your older Carrier might be the same tonnage but it had to deal with an improper plenum.

    Looking at your attachment... the humidity is ranging around 50-60% which isn't uncommon. How long does your AC stay on before it cycles off?
    You can call me Sam

    It should be a crime to be a mechanical engineer in San Diego
    Summer Design Temperature: 83 F Dry Bulb ~ 69 F Wet Bulb (California Climate Zone 7)

  4. #4
    Join Date
    Dec 2005
    Posts
    2,032
    Post Likes
    10 days plotted (squeezed) on that graphic is horrible. How can one read and interpret that graphic?
    We are NOT at your house. So without data of the unit performance, we cannot give you advice. Besides, call the contractor back since you are not 100% satisfy.

  5. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes
    Quote Originally Posted by CoastalWGSD View Post
    Hey all...I was out here in June and early July investigating options for replacing my older Carrier, 3 ton, 13 SEER HVAC system (outside unit was very noisy and had a hard start added to it, but we felt we were on borrowed time).

    Long story short, we went with installing a new air handler (same variable speed, etc) and a new outside unit (Carrier, 3 ton 16 SEER upgraded outside "cage")

    We still experienced the same issues over the next 30 days and had the company sales rep come back out. He used some commercial readers (sticks that read temp, humidity and some other stuff) and left them in two different rooms over a period of 10 or so days.

    They just sent us a copy of one of the data results and the temp only varied by 3 degrees, but the humidity varied considerably (up to 61.1% - varied a lot)...

    Does anyone have any suggestions as to what could be causing this new system to feel like it
    isn't doing as good of a job as my old failing 13 SEER Carrier system???JamesRiverAir_HVAC_MonitoringReport.pdf
    Relative humidty at 51+/- 3% at 72'F seems near constant and close to meat locker conditions.
    My 78'F at 42% R.H. is very comfortable.

    Ultra-Aire dehumidifier unit is needed if you wish to operate at the lower 70's 'F.
    http://www.ultra-aire.com/index.php?...id=65&Itemid=5
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    and close to meat locker conditions.
    LOL, you wouldn't like how cool I keep my place then.

    72°F and 48%RH.

    OP, do you have a VS blower.

  7. #7
    Join Date
    Jan 2007
    Location
    Jacksonville,Fl
    Posts
    133
    Post Likes
    Quote Originally Posted by beenthere View Post
    LOL, you wouldn't like how cool I keep my place then.

    72°F and 48%RH.

    OP, do you have a VS blower.
    Same here, I should probably live up North for as cold as I like in the house

  8. #8
    Join Date
    Jun 2012
    Posts
    23
    Post Likes
    Thread Starter

    @Sam

    Quote Originally Posted by hcong View Post
    The general question that everyone asks is did you get a load calculation done? Humidity problems are usually due to oversized units. Higher electricity bills may also mean shorter on cycles because of oversized units. Your older Carrier might be the same tonnage but it had to deal with an improper plenum.

    Looking at your attachment... the humidity is ranging around 50-60% which isn't uncommon. How long does your AC stay on before it cycles off?
    Sam,
    I am no pro...I learned most of what I think I know from this site! I KNOW that my old unit that was limping with a hard start kit kept my house nice and cool and an even 72 degrees year round. I KNOW that this new unit doesn't seem to do that. I was told that the humidity can make the 72 degrees showing on the thermostat feel warmer than 72 (which makes some sense, but my other thermostat on my fireplace remote says otherwise. It states that it is 74 to 75 degrees when the thermostat for the HVAC says 72...The only differences in the old unit and the new unit is that the old one was 13 SEER and the new one is 16 SEER...They both had/have a variable speed air handler (same model, but new one with new system)...The Plenums that were added are about 18" x 18" I think, haven't measured them, but that is what I am guessing with what I saw. The old system didn't really have a true plenum, but had a 90 turn on the return side...I think it had a regular plenum on the supply side...

    As far as cycling...Havent really sat here and waited for it to turn on and off and am not sure I would know when it is cycling...

  9. #9
    Join Date
    Jun 2012
    Posts
    23
    Post Likes
    Thread Starter
    I agree on trying to read the data squeezed in like that...I am in touch with the sales rep and the company has been very cooperative about coming out and checking out the system the first call...My concern is that they had to replace the defrost board (motherboard) on a brand new unit...I wonder if that part is still not working correctly...

  10. #10
    Join Date
    Jun 2012
    Posts
    23
    Post Likes
    Thread Starter
    meat locker conditions? Guess it depends on how thin your skin is! LOL! I have always had it at 72 degrees...What the relative humidity has never come into play until they put the readers in the house to determine system variation...

  11. #11
    Join Date
    Jun 2012
    Posts
    23
    Post Likes
    Thread Starter
    @second opinion
    I do have tickets from them...We are in central VA, what info would I be looking for?
    This is what I have from their QC checklist visit

    Line Set Size 7/8-3/8
    Method of Charging Subcool
    Evacuated to Microns 176
    Amount Ref +/- 10 oz
    Temp Split In 76 Temp Split Out 57
    Ref Pressure (lbs) Suction 140 Dischard 275
    Static Pressure Supply .20 Return .40

    I had the sales rep come out again with their lead tech on 8/13 and that is when they decided the defrost board needed to be replaced. I have no numbers from that visit or the visit after they replaced the boards except the diagram of readings from the inside monitors they left here for 10 days...

  12. #12
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    72 and shuts off, or 72 and never shuts off? If it hits 72, shuts off, and you arent comfortable then set it to 70! Some people require thermostats to tell them they are comfortable, and obsess when the number doesn't rigidly conform to their preconceptions. (when I run into one of them, I game the stat. Good stats let you tell ho what they want to see.)

    Size of this house?

    By the chart it appears there are a lot of cycles. Hcong said it first, grossly oversized.

  13. #13
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    What are the model numbers of the indoor and outdoor unit, what thermostat do you have? If its the variable speed airhandler I think it is, there are some adjustments to it.
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  14. #14
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    ... Oh, my comfort numbers are more in line with Dans, 78f at 40rh, 76 at 45, need it cold for high rh, but it ain't what id call comfortable.

  15. #15
    Join Date
    Jun 2012
    Posts
    23
    Post Likes
    Thread Starter

    System info for beshvac

    Quote Originally Posted by beshvac View Post
    What are the model numbers of the indoor and outdoor unit, what thermostat do you have? If its the variable speed airhandler I think it is, there are some adjustments to it.
    Carrier 25HCB3 Heat pump/AC -outside
    Carrier FV4 air handler under house in crawl space
    I can't recall model number but the Thermostat is a Honeywell which raises questions for me as the variable speed air handler specifies a Carrier Thermidistat

  16. #16
    Join Date
    Jun 2012
    Posts
    23
    Post Likes
    Thread Starter
    It ALWAYS reads 72 I have never seen it go up to 73, but it does come on and off throughout the day...I would say in the last week, it is at 72 and keeps running when temp outside is higher....
    Soze of the house is 1800 square feet (ranch)

    The HVAC rep tweaked the controls on the variable speed air handler and I don't know what exactly they did, but it sounded like he reduced air flow...

  17. #17
    Join Date
    Jun 2006
    Location
    Richmond, VA
    Posts
    4,184
    Post Likes
    Quote Originally Posted by CoastalWGSD View Post
    Carrier 25HCB3 Heat pump/AC -outside
    Carrier FV4 air handler under house in crawl space
    I can't recall model number but the Thermostat is a Honeywell which raises questions for me as the variable speed air handler specifies a Carrier Thermidistat
    That's only a 13 seer condenser with the fv002 or 003 airhandler which is 14 or 14.5 seer rated. it has controls to adjust the airflow for better humidity control, which is unknown from not knowing what thermostat.
    I wish I had a $1.00 for every response I deleted.....

    "Decidedly Superior in a twisted pathetic way".....

  18. #18
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    1800 sf ranch, 3 ton. Sigh. That's a shame, when you were here earlier didn't anybody caution against over sizing? Did anybody recommend an Infinity system?

    For reference, think your ranch is built better, worse, or about the same as a double wide trailer of the same size?

    I have a client with such a residence with 1.5 ton heat pump. (BTW, we can on rare occasions hit 100f, and we get more sun/solar gain/longer days than southern folks.)

    So humidity is likely to be a problem under all but hottest conditions because your unit cools faster than it dehumidifies. This bears repeating because people unfortunately want "cool quick" which is actually the opposite of comfortable cool. Over sized units cool faster than they dehumidify. Comfortable cool is slow, dehumidifying faster than cooling type of cool.

    Probably need an edge thermostat to manage fan speed, that might help some. It can slow airflow across the coil, making it colder, making it pull more moisture. And maybe a cooler set point.

  19. #19
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Quote Originally Posted by skippedover View Post
    Finally, you may want to consider that all of the Carrier air handlers, except for one or two 'builders models', have ECM motors in them. These motors are intended to reduce electrical consumption but if installed in a high static duct system, can have the opposite result. So selecting a company that does a proper load analysis (Manual 'J') and duct evaluation (Manual 'D') before recommending a replacement system is in your best interest.
    Skip is one of the most experienced Carrier guys out there. This suggestion was in your original request for help last spring.

    Then in July you asked a product question about performance and comfort series, apparently confusing the two levels as one:

    I wanted the Carrier Performance Comfort Series
    When I looked into the above Model numbers, they seem to be the bottom or base models that Carrier has...
    Also not sure if we would benefit from two stage...
    (Guess THAT question is answered... Wonder if they'll let you upgrade.)

    And now you are having problems that likely relate to NOT having a load calc or duct diagnostics. (Dollars to doughnuts a 2 ton system would have not only cost less, you wouldn't be having these troubles.)

    What are we doing wrong not helping people avoid these train wrecks? What words are we not using? Seeing this over and over again is driving me nuts!

  20. #20
    Join Date
    Jun 2012
    Posts
    23
    Post Likes
    Thread Starter
    Ranch is in no way built like a double wide...Tall crawl space, originally had 3 ton 13 seer and never had this issue! Concrete and brick foundation. LOTS OF WINDOWS, all checked for seal and checked out great. Did not have this issue at all for the 12 years we had the first unit!

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •