    Whats the procedure recommended for checking the motor windings on any 3 phase compressor? Thanks

  2. #2
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,856
    Ohm out the windings, all readings should be equal and nothing to ground.
    Karst means cave. So, I search for caves.

  3. #3
    Join Date
    Oct 2006
    Posts
    23
    Thanks! Loud and clear!((())) I show no reading to ground,However it is a direct short.Perhaps turn to turn
    at the windings,which should show up when the resistence is measured at the windings...I assume.