  1. #1

    HP Blower Motor tries but won't run

    York HP installed in 2003. AC supposed to be running. We started to hear clicking while the outside unit was running but the blower was not. I went under the house and checked the little fuse(It was Ok). I checked to find the source of the clicking. It is coming from the fan motor trying to start. The fan tries to move but won't move more than 1/4 inch with each click. The fan would turn fairly freely with help but not keep going. This motor has two plastic plugs to hook up the bundle of wires. After several minutes, a sharp alarm sound was heard(beep beep). The green light on the circuit board was flashing while the fan was trying to start. The outside unit was running and the air handler coil began to freeze. We tried the "fan on" setting with the same results. I did some research and went back under to look for a run capacitor. There was none that I could see- none on the fan housing and nothing on the circuit boards that looked like a capacitor. Everything I read said there would be a capacitor.


    What should I do next?
    Is there a capacitor I can't see?
    What does the green flashing light mean when the power was on?
    What does that alarm sound(beep beep, like a microwave oven) mean?

    I will appreciate any worthwhile advice.

  2. #2
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,051

  3. #3
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,158
    What model number is the outdoor unit?

  4. #4
    Model E4H036S06A Stellar Plus

  5. #5
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,158
    Quote Originally Posted by Mr Bill View Post
    A unit that old, I would just stick a PSC in it and be done.

  6. #6
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,073
    Quote Originally Posted by just_opinion View Post
    I thought NO DYI
    We're is the line in DIY anymore.


    Sent from my iPhone using Tapatalk.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  7. #7
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    1,629
    Check your warranty. I don't know about york but most of the ECM motors I deal with have a 10 year part warranty. Changing a module on one takes a half hour so the labor won't be much.

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,330
    It should have a 10 year warranty. But, 2003 was when they were just going to the 10 year, so his may not be covered.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,051
    Model number of indoor and outdoor units may help to select replacement blower motor.

    Yes a new different one will have to be installed.

  10. #10
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,330
    Quote Originally Posted by SBKold View Post
    Model number of indoor and outdoor units may help to select replacement blower motor.

    Yes a new different one will have to be installed.
    A module replacement is about the same cost as a blower motor replacement. And doesn't need the relay addition that converting to a PSC motor would.

    Plus, if he's in a humid area, he may not like the humidity increase he could get from going to a PSC motor.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,158
    I just realized he was talking of the indoor blower instead of the condenser motor. In that case I would definitely go back with original parts.

  12. #12
    Thanks for all the input. The only warranty now is on the compressor. The rest ran out at 5 years. What is the official name of the "module"? Fan control module?

  13. #13
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,330
    No, its an ECM module, and its OEM only.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event