Thread: How much make up air?
-
09-18-2012, 07:19 AM #1
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
How much make up air?
Hi,
I would love any help you could give me with regards to deciding how much make up combustion air i need for my master bedroom area. The natural gas, room air fed units are a 90% 80k btu furnace (oversized), and two (overkill) 50 gallon hot water heaters, in a 700 sq ft unfinished basement (insulated ceiling).
It connects via an open 3/4 door passage to an area where my wife works out (rarely i must add). There were two screens in place of concrete blocks for vents in the equipment room. In winter the equipment area is freezing cold, and the cold drifted over to my wife's workout area. I perhaps stupidly sealed off the two screen vent/holes.
I would love to have the minimum safe air possible. What would i need in winter? Maybe just one open. What about summer (only the hot water heaters).
Thanks
Steve
-
09-18-2012, 07:51 AM #2
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
09-18-2012, 08:07 AM #3
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
Second opinion, thanks. Not sure. They are 50 gallon. Standard type, bradford white i believe. Not super efficient or anything.
-
09-18-2012, 08:47 AM #4
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
I can check tonight if that helps.
-
09-18-2012, 09:26 AM #5
Professional Member*
- Join Date
- Mar 2009
- Location
- Mount Holly, NC
- Posts
- 1,614
so, basically you have 170Kbtuh of gas appliance input. you will need to supply air to. there also needs to be a HIGH and a LOW combustion air source.
The TRUE highest cost system is the system not installed properly...
The three big summer hearththrobs...
Mel Gibson
Dwane Johnson
The A/C repairman
-
09-18-2012, 06:56 PM #6
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
Well would two, or preferably one, screens instead of block be enough? (16x8 each i'm guessing). It would be about 25 feet away, and certainly not low and high.
I guess i wouldn't care if I could put a door to the room, but there are the water pipes and the water heaters. The room gets its heat passively mostly from the other room, (which gets it from lack of insulation b/t the study above). A stupid arrangement.
thanks
Steve
-
09-18-2012, 06:58 PM #7
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
Another question would be what would i need for only the hot water heat. I will eventually replace the 80k with a 40k york modulator.
-
09-18-2012, 07:23 PM #8
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
09-18-2012, 07:36 PM #9
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
Second Opinion, thank you.
Both HWH are 40k each, total of 80k. The furnace is 80k.
Perhaps not relevant, but the space is 1,000 sq ft (maybe 1500 is you include the non-insulation/drift to part of the basement.) So the furnace is only running in short bursts. The hot water heaters are for the "whirlpool" tub, which is never used, and the over the head huge shower rain-like head, also never used. It looks great in the ads, but water pouring straight down runs over the face and eyes, really not pleasant. But I guess it might be used so I should plan enough air for them both on full draw.
Steve
-
09-18-2012, 07:37 PM #10
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
Oh, the unit uses room air, but has a pvc pipe to vent. (a 1995 trane xe90).
-
09-18-2012, 08:10 PM #11
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,251
2006 INTERNATIONAL MECHANICAL CODE
http://www2.iccsafe.org/states/newje...tion%20Air.pdf
DO IT RIGHT AND DO IT COMPLETELY RIGHT.!
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
09-18-2012, 09:04 PM #12
Regular Guest
- Join Date
- Apr 2012
- Location
- Princeton NJ
- Posts
- 119
dan sw fl:
Thanks! 1995 construction, w/dryvit on the exterior walls (super tight), but no spray foam or anything special in the attic or basement area. Would you agree that i'm "not unusually tight".
If that's the case, i could leave it as is, no outside air. The 3/4 door size passage way is more than 1 sq inch/1k btu. To be safe may I will leave a 7x7 inch opening in the block screen (1 sq/4k btu).
Thanks
Steve
Thanks.
-
09-18-2012, 09:16 PM #13
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251


Reply With Quote