    Least Restrictive 4" Media

    What is the lowest pressure drop 4" media filter out there? I am using a Columbia MERV 8 right now and the damn thing is responsible for a .2 drop, What! This system is inverter driven and I need to get the static pressure at least .1 lower or the EEV wont allow full capacity. Thanks
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  2. #2
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,611
    Post Likes
    What is the feet per minute across the filter?
    The Glassfloss is .25" @ 500FPM.
    http://www.glasfloss.com/Pleated%202012.pdf

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,993
    Post Likes
    .1 over a 4" media probably won't happen unless you are using a 20x25 at 100 CFM

    On our system 20x25 Aprilaire was .23" clean at 1600 CFM. New 1" was .5 for compariston.

  4. #4
    Join Date
    Sep 2009
    Location
    Kennesaw, GA
    Posts
    757
    Post Likes
    Quote Originally Posted by 54regcab View Post
    What is the feet per minute across the filter?
    The Glassfloss is .25" @ 500FPM.
    http://www.glasfloss.com/Pleated%202012.pdf
    Good filter. I have that in my system at home.

  5. #5
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,611
    Post Likes
    Quote Originally Posted by mofotech View Post
    Good filter. I have that in my system at home.
    I use them also, one of the best value 4" filters IMHO.

  6. #6
    Join Date
    Aug 2011
    Location
    Eastern Shore, MD
    Posts
    802
    Post Likes
    Quote Originally Posted by LibertyTree View Post
    What is the lowest pressure drop 4" media filter out there? I am using a Columbia MERV 8 right now and the damn thing is responsible for a .2 drop, What! This system is inverter driven and I need to get the static pressure at least .1 lower or the EEV wont allow full capacity. Thanks
    i had the same issue....what i did was put 2 20x25 4" in...now i have a .07" drop!

  7. #7
    Join Date
    Aug 2011
    Location
    Eastern Shore, MD
    Posts
    802
    Post Likes
    Name:  filter rack.jpg
Views: 76
Size:  43.0 KB