    Line set size problem

    We have a leaking coil. About 9 years old, Trane 4ton. The tech noticed the suction line was spliced when installed new, but they spliced a length of 5/8 with 7/8. The whole run is about 80' with about half at 5/8". There is another problem in that the condensers were installed flip-flopped, so we've been running a 3ton condenser on a 4ton coil with 5/8 and 7/8 suction line for years. Add to that duct and plenum problems and you get the jist of my angst. I'm assuming the line set should be replaced,(?) it's just a bear to get to and running outside would look horrible even using a downspout or conduit. The condenser will either get replaced or swapped with the other which is 3 1/2 ton which has been running on a 3ton coil. Welcome to metro Atlanta new construction problems...

  2. #2
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    4,437
    Post Likes
    For many reasons you should find a way to change that lineset.
    ...

  3. #3
    Join Date
    Sep 2012
    Location
    North of Atlanta
    Posts
    8
    Post Likes
    Thread Starter
    Thanks- looked at it some more today. They may need to cut a little drywall- but it's doable. Anything I should watch for to make sure they're doing it right? Is it standard practice to splice line sets (of the same size this time) or should it be one piece?

    Thanks much

  4. #4
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    80ft would most likely not be 1 piece lineset anyway's. I would let them cut the 5/8ths out and put in the 7/8th's.
    It's hard to stop a Trane. but I have made one helluva living keeping them going.

  5. #5
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,402
    Post Likes
    Quote Originally Posted by de63 View Post
    Thanks- looked at it some more today. They may need to cut a little drywall- but it's doable. Anything I should watch for to make sure they're doing it right? Is it standard practice to splice line sets (of the same size this time) or should it be one piece?

    Thanks much
    You can have a splice in your lineset. I agree with Southern Mech -- it may make more sense to just remove the 5/8" portion and replace it with 7/8", depending on the access. Lines should be fully evacuated using a micron gauge to ensure no leaks.

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    They may have used the 5/8 to 7/8 to help the oil return to the compressor.

    You may notice humidity changes when you put the 3.5 on the 4 ton coil, and when the 3 ton is put on the 3 ton coil.

  7. #7
    Join Date
    Sep 2012
    Location
    North of Atlanta
    Posts
    8
    Post Likes
    Thread Starter
    Humidity is important to control in GA. Which setup gives the best dehumidification? Keep in mind the unit cycles often in our hot summers. The first floor has a 3 1/2 ton condenser and 3 ton coil. Will putting a 3 ton condenser improve dehumidifying?

    RE: line set to the second floor- the first five feet off the condenser is 7/8", then the next 40' is 5/8 which is mostly vertical up to the attic and then back to 7/8" horizontally to the coil for 35' feet or so. On paper this would not be good for a 3 1/2 to 4 ton unit, correct? If they did it on purpose, not sure why. If it is usable, it would save me some $$.

    Thanks in advance for all insight

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Is it 5/8, or is it 3/4".

    The 3.5 on a 3 ton coil may be giving you better moisture removal then a 3 ton on a 3 ton will.

  9. #9
    Join Date
    Sep 2012
    Location
    North of Atlanta
    Posts
    8
    Post Likes
    Thread Starter
    I measured them as 7/8" OD and 5/8" OD.

    I may just leave the 3.5 on 3 then, scrap the 3 ton and upgrade to a 4ton, which is what the load calc called for. (3.8 anyway)

    Thanks

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    How well does, or doesn't the 3 ton maintain temp.

  11. #11
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    1,025
    Post Likes
    You might check the size again. Are you sure it is 5/8 and not 3/4?
    Blue Fox

  12. #12
    Join Date
    Sep 2012
    Location
    North of Atlanta
    Posts
    8
    Post Likes
    Thread Starter
    The system really only struggled for cooling on the hottest days. It dehumidified just okay but there are return air and duct balancing issues compounding the problem. The extremity rooms suffered the most of course.
    I'll check the size again, the tech said 5/8". Could be 3/4". Good question.

  13. #13
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    I agree with the other posters: You really need the 7/8 lineset ALL the way between the units... builders do sometimes allow their subs to not do what should be done. Happens when granite countertops, SS appliances, and tile floors are more important than installed things like heat and AC.

    Usually (but not always) a slightly larger coil on a properly sized outdoor unit (assuming the ductwork is sized properly) will provide better humidity control... however a VS drive furnace is the better solution.

    The wise thing to do is start with the basics:
    Load Calc, then duct evaluation, then equipment sizing. (Note if this were new construction, the equipment sizing would come second with duct sizing to fit the equipment).

    Usually, when one tries to 'fix' something by 'working around' given parameters... they either live to regret it... or end up spending too much $$$ 'experimenting'... Neither is a good solution.

    Go back to the basics, follow them, and you will have a system working as it should... to handle the load. And get a contractor that will do the same.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  14. #14
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    If the 7/8" part of the suction line is accessible, and a 3.5 ton system is big enough, you could have it changed to 5/8 and have a Daikin Inverter Ducted system installed.
    http://www.daikinac.com/residential/...oducts&page=57

  15. #15
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by de63 View Post
    The system really only struggled for cooling on the hottest days. It dehumidified just okay but there are return air and duct balancing issues compounding the problem. The extremity rooms suffered the most of course.
    I'll check the size again, the tech said 5/8". Could be 3/4". Good question.
    Correcting the air balance issues may allow the 3 ton to handle the load much better.

  16. #16
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Quote Originally Posted by mark beiser View Post
    If the 7/8" part of the suction line is accessible, and a 3.5 ton system is big enough, you could have it changed to 5/8 and have a Daikin Inverter Ducted system installed.
    http://www.daikinac.com/residential/...oducts&page=57
    Hmmm, I have heard about these; They use a Daiken outdoor unit and a re-branded Goodman AH?

    If so, could this be used as a replacement for a conventional system?
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  17. #17
    Join Date
    Sep 2012
    Location
    North of Atlanta
    Posts
    8
    Post Likes
    Thread Starter
    Yup, just re-verified- 5/8 OD soldered to 7/8 OD for what should be a 3.5 ton cond. on 4 ton coil...lovely, isn't it?...

    guess they're fishing a new line. I'll go ahead and replace the whole run since we'd be switching from R22 to R410.

    A cheaper solution is to replace just the coil and line set, swap the units and recharge with R22 again. Thoughts on that? Has the 3-ton unit been stressed too hard sucking through a 5/8" pipe for 9 years?

    Bite the bullet and go R410 with a new unit so the new coil isn't a throw away should the condenser bite it in a year? The unit 'looks' in good shape, but couldn't tell you anything more.

  18. #18
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Quote Originally Posted by ga-hvac-tech View Post
    Hmmm, I have heard about these; They use a Daiken outdoor unit and a re-branded Goodman AH?

    If so, could this be used as a replacement for a conventional system?
    We may be seeing a lot more of these! Id like to see some Info on them.

  19. #19
    Join Date
    Sep 2012
    Location
    North of Atlanta
    Posts
    8
    Post Likes
    Thread Starter
    Okay, to summarize where we are now. The 4 ton coil will be replaced(leaking), line set will be replaced(wrong size). Looking for feedback on whether we should keep the condensors and just swap them so they are with their correct respective coils. Any way to test the 'wear and tear' on a compressor? or leave the 3.5 ton on the 3 ton coil and replace the 3 ton with a new 3.5ton which would then be R410.

    Open to suggestions.....thanks

  20. #20
    Join Date
    Sep 2005
    Posts
    58,702
    Post Likes
    Quote Originally Posted by de63 View Post
    Okay, to summarize where we are now. The 4 ton coil will be replaced(leaking), line set will be replaced(wrong size). Looking for feedback on whether we should keep the condensors and just swap them so they are with their correct respective coils. Any way to test the 'wear and tear' on a compressor? or leave the 3.5 ton on the 3 ton coil and replace the 3 ton with a new 3.5ton which would then be R410.

    Open to suggestions.....thanks
    From post #13:
    The wise thing to do is start with the basics:
    Load Calc, then duct evaluation, then equipment sizing. (Note if this were new construction, the equipment sizing would come second with duct sizing to fit the equipment).

    Usually, when one tries to 'fix' something by 'working around' given parameters... they either live to regret it... or end up spending too much $$$ 'experimenting'... Neither is a good solution.

    Go back to the basics, follow them, and you will have a system working as it should... to handle the load. And get a contractor that will do the same.
    (end)

    If I had a $1 (inflation you know, nickels are worthless) for every time someone was too busy or cheap to do the basics... and ended up with a big mess... I could buy a new van.

    Do the basics! And if your contractor will not (or does not know how), then get a contractor that does.

    Sorry to be blunt... however the quality and comfort of your system, as well as the energy bills will depend on doing the basics and doing them properly.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •