Intelipak Remote pot.
Does anybody know what the ohms value Trane likes for the remote economizer minimum position. I think it is TB-14 terminal 8 and 9, but the 135ohm kele control that is hooked up has no effect on the position. Is is programming or the wrong ohm value? Any advice?
I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
09-16-2012, 12:11 PM #2
i don't believe that there is a TB14...i guessed at one of the 78,474 different model numbers that make up Intellipaks but then I gave up.
The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
I know a famous song that ends in 'my nose'. The artist is dead. Know who?
-
09-16-2012, 01:37 PM #3
I believe it's 270ohm. Also, you need to set the default OA min position setpoint source to remote pot. It's under setpoints>setpoint source.
-
09-16-2012, 07:44 PM #4
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
I will give it a try. I am tempted to purchase the remote pot from Trane just to see what the ohm value is.