    Intelipak Remote pot.

    Does anybody know what the ohms value Trane likes for the remote economizer minimum position. I think it is TB-14 terminal 8 and 9, but the 135ohm kele control that is hooked up has no effect on the position. Is is programming or the wrong ohm value? Any advice?
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,336
    i don't believe that there is a TB14...i guessed at one of the 78,474 different model numbers that make up Intellipaks but then I gave up.
    "Mother" is the name for God on the lips and hearts of children....The Crow

  3. #3
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,333
    I believe it's 270ohm. Also, you need to set the default OA min position setpoint source to remote pot. It's under setpoints>setpoint source.

  4. #4
    Join Date
    Nov 2005
    Posts
    1,350
    I will give it a try. I am tempted to purchase the remote pot from Trane just to see what the ohm value is.