+ Reply to Thread
Page 1 of 2 12 LastLast
Results 1 to 20 of 26

Thread: Just some thougts about chillers

  1. #1
    Join Date
    Nov 2011
    Location
    North sweden, Umeε, Where the birches growing without limits.
    Posts
    138
    Post Likes

    Just some thougts about chillers

    Well, i have fighted against a "yurk" chiller (loaded with R407C, yes i hate that refrigerant) that's trippin' on the freeze guard at one circuit, +3c (okay it'ts pure water on the cold side, a +12c/+8c system) Both circuits is a little underfilled, just about to flash in the sight glass.

    However.... Suspicious about flow issues. Both circs is running with almost same values (+3c evap/+40c cond) but the circ thats trippin on freeze guard is running with deltaT 7c in/out on the water side, +3c subcool, +4c superheat, the other circ is +4c sub, +5 superheat and 5c deltaT in/out water side (yup it's plate heat exchangers), my service leader meaned that I would get a lower deltaT on the "problem circ" if I refilled it with refrigerant. But in my book... I would get a higher deltaT if its "Topped up" with missing ref., to get a lower dT, remove some ref. you get less effiency. I know that's its more factors that's making sense. But now. Just focusing on the ref. filling...

  2. #2
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Heee de gig a doo dur dee ger de dig a doo , her dier gig a doo dur murg murg murg murg .
    Muppett show Swedish chef .
    Sorry couldnt help myself its Friday .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  3. #3
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    Wtf?

  4. #4
    Join Date
    Aug 2012
    Location
    Toronto, Canada
    Posts
    82
    Post Likes
    Quote Originally Posted by supertek65 View Post
    Wtf?
    X2... Deep breath and try that again

  5. #5
    Join Date
    Nov 2011
    Location
    North sweden, Umeε, Where the birches growing without limits.
    Posts
    138
    Post Likes
    Thread Starter
    Pls, no f-ing garbage in the thread thank you!

    And.... Because of european stupid laws we're not allowed to use cfc and hcfc's, if we do, bye bye license for fluorated refs... (but private there's no problems )

    Yes i know that cfc's is harmful for the ozone layer, but it's probably the better refs

  6. #6
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  7. #7
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    1) Why do you hate 407C? It's just a blended refrigerant - it hasn't done anything to you, has it?
    2) Sounds like you may have heat transfer issues. Probably be a good idea to look at flow first, obstruction next, depending on how the waterside is piped.
    3) Don't want to be the "ugly American", but since this is a U.S. based forum, you might want to convert your temps to °F before posting. I, for one, won't go to any great lengths to do that for you, and I know a lot of others that feel the same, so you limit your assistance by using the metric system around here.

  8. #8
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by klove View Post
    Don't want to be the "ugly American", but since this is a U.S. based forum, you might want to convert your temps to °F before posting. I, for one, won't go to any great lengths to do that for you, and I know a lot of others that feel the same, so you limit your assistance by using the metric system around here.

    X2.....

    You will get a lot more responses if you convert to deg F. And you can't convert the delta T, you have to convert the 2 temps to deg F then figure delta T.

  9. #9
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    361
    Post Likes
    Quote Originally Posted by R123 View Post
    X2.....

    You will get a lot more responses if you convert to deg F. And you can't convert the delta T, you have to convert the 2 temps to deg F then figure delta T.
    For delta T C to delta T F you can multiply by 1.8 or divide by 1.8 to go from delta F to Delta C. Living in a metric system country and communicating with US factories you get nowhere quick if you cannot be fluent in both languages
    Necessity is the mother of invention

  10. #10
    Join Date
    Nov 2011
    Location
    North sweden, Umeε, Where the birches growing without limits.
    Posts
    138
    Post Likes
    Thread Starter
    Repost from original post now with farenheit scales

    Well, i have fighted against a "yurk" chiller (loaded with R407C, yes i hate that refrigerant) that's trippin' on the freeze guard at one circuit, +37f (okay it'ts pure water on the cold side, a +53f/+46f system) Both circuits is a little underfilled, just about to flash in the sight glass.

    However.... Suspicious about flow issues. Both circs is running with almost same values (+37f evap/+104f cond) but the circ thats trippin on freeze guard is running with deltaT 12,5f in/out on the water side, +5,5f subcool, +7f superheat, the other circ is +7,2f sub, +9 superheat and 5c deltaT in/out water side (yup it's plate heat exchangers), my service leader meaned that I would get a lower deltaT on the "problem circ" if I refilled it with refrigerant. But in my book... I would get a higher deltaT if its "Topped up" with missing ref., to get a lower dT, remove some ref. you get less effiency. I know that's its more factors that's making sense. But now. Just focusing on the ref. filling...


    Oh... about my 407C issues... Ok, it might be a good ref. But not for me, i hate refs with big glide. I rather run 134a, 404A (or even better, 507) or 410A, ok 410 uses higer pressures, but that's no problem for me.

  11. #11
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    What kind of York chiller? Air cooled, water cooled, recip, screw, scroll? What's the model number? When you say "freeze guard at one circuit" what do you mean? I would think that would mean low water temp cutout, but that would shut down the whole chiller, not just a circuit. Do you mean "low evap refrigerant temp"?

  12. #12
    Join Date
    Nov 2011
    Location
    North sweden, Umeε, Where the birches growing without limits.
    Posts
    138
    Post Likes
    Thread Starter
    water/water, hermetic reciprociating comp, ycwm 150. there's 2 circuits in the chiller, both circs has own plate heat exc's for cold and warm side, the only thing that ties them together is incoming and outgoing water pipes.

    the freeze guard is sensing the liquid (water) temp in the plate exch., tripping the circ that's have too cold liquid temp, if there's flow problem etc.

    ah... the circs is independent of each other...

    got me?

  13. #13
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    flow issues could be the problem. is the safety calibrated and tripping at the setpoint? how are the pressures as it is pulling the load down...stable and steady or losing control and 'wild'? keep in mind that R407c has a very high temperature glide and you must use the appropriate scale for liquid or vapor measurements. i wish we would all go metric...its a lot easier after you get used to it.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  14. #14
    Join Date
    Nov 2011
    Location
    North sweden, Umeε, Where the birches growing without limits.
    Posts
    138
    Post Likes
    Thread Starter
    It sometimes trippin at set point, but often at freeze guard. The pressures is stable and vaporize is following the water temp as it should do. Nothing uncontrolled. My REFCO 4-way manifold has vapour and liquid scales. Checking the gauges several times per year against a digital reference gauge.

    But yeah sure it's flow issues, a colleauge of mine is maybe going to clean the plate exchangers. All depends on the customer.

  15. #15
    Join Date
    May 2002
    Posts
    949
    Post Likes
    What's your evap approach?
    assuming the charge is correct per manufactures guidelines.
    Leaving water minus sat suction temperature. You said sat suction was +37 ,what's your leaving water ? 45????

    Example
    45
    -37
    = 8 approach

    Compare both circuits .

    If the approach is normal suspect low flow ,if the approach is high suspect fouling.

  16. #16
    Join Date
    Nov 2011
    Location
    North sweden, Umeε, Where the birches growing without limits.
    Posts
    138
    Post Likes
    Thread Starter
    Faulty circuit
    Evap +37f, leaving water +38,3f app=1,3f

    Correct circuit
    Evap +37f, leaving water +41f app=4f

    what is a correct approach?

  17. #17
    Join Date
    May 2002
    Posts
    949
    Post Likes
    That approach doesn't sound out of line .

    The normal approach is something you could find in the machines or heat exchangers design / build documents as it can vary.

    I've seen approaches on fouled coolers upwards of 20 degrees !

    I have another question (s)

    Why is your water getting down to 37? is that setpoint ?

    What is your water temp setpoint? if your running water and not antifreeze your asking for trips at 37, in my opinion.

    Are you controlling temp by leaving water temp or entering water temp?

    What is the freeze trip setpoint ? See next question

    Are you running glycol/antifreeze or plain water?
    If antifreeze can you configure the machine as so and lower the trip setpoint

    I am used to seeing trip points in the area of 36 for water which you are very close to.

  18. #18
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Also re-reading your posts I doubt you are fouled, but it is something to eliminate out of the equation.

    You have a 9 degree td across the "good" circuit and 12.5 across the "fail" circuit

    Read my above post and answer those questions if not only to yourself .

    you may have flow issues, but I still wonder why you are running a chiller so close to the freeze trip point . In my opinion your asking for nuisance trips .

    I would like to see your answer to my questions.

  19. #19
    Join Date
    Nov 2011
    Location
    North sweden, Umeε, Where the birches growing without limits.
    Posts
    138
    Post Likes
    Thread Starter
    Set point is 46f, starts at 53f. It's starting and stopping on inlet temp. Pure water, no antifreeze, no filters or anything like that

    Anyhow, putted some loggers on both circuits. Correct circ having parallell curves, faulty circ having uneven curves, directly the machine starts the outlet is dropping to 37-38f and lays there until inlet temp is correct, or trips on freeze guard.

    Mikeacman: Everything about the set temps etc... is written in previous posts.

    The company that I'm doing the job for have several systems with this type of system and chillers. Just clean freshwater.

  20. #20
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Hmmmmm.

    looks like a flow issue but

    Can measure a pressure diff and calculate gpm and compare both circuits ?

    Is your flow fluctuating ? VFD ramping up and down the pump?

    I guess for a temp measure you could raise the setpoint a few degrees until you figure it out.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •