    Just some thougts about chillers

    Well, i have fighted against a "yurk" chiller (loaded with R407C, yes i hate that refrigerant) that's trippin' on the freeze guard at one circuit, +3c (okay it'ts pure water on the cold side, a +12c/+8c system) Both circuits is a little underfilled, just about to flash in the sight glass.

    However.... Suspicious about flow issues. Both circs is running with almost same values (+3c evap/+40c cond) but the circ thats trippin on freeze guard is running with deltaT 7c in/out on the water side, +3c subcool, +4c superheat, the other circ is +4c sub, +5 superheat and 5c deltaT in/out water side (yup it's plate heat exchangers), my service leader meaned that I would get a lower deltaT on the "problem circ" if I refilled it with refrigerant. But in my book... I would get a higher deltaT if its "Topped up" with missing ref., to get a lower dT, remove some ref. you get less effiency. I know that's its more factors that's making sense. But now. Just focusing on the ref. filling...

  2. #2
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,022
    Heee de gig a doo dur dee ger de dig a doo , her dier gig a doo dur murg murg murg murg .
    Muppett show Swedish chef .
    Sorry couldnt help myself its Friday .
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  3. #3
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,832
    Wtf?

  4. #4
    Join Date
    Aug 2012
    Location
    Toronto, Canada
    Posts
    81
    Quote Originally Posted by supertek65 View Post
    Wtf?
    X2... Deep breath and try that again

  5. #5
    Join Date
    Nov 2011
    Location
    North sweden, Ume, Where the birches growing without limits.
    Posts
    94
    Pls, no f-ing garbage in the thread thank you!

    And.... Because of european stupid laws we're not allowed to use cfc and hcfc's, if we do, bye bye license for fluorated refs... (but private there's no problems )

    Yes i know that cfc's is harmful for the ozone layer, but it's probably the better refs

  6. #6
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,022
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  7. #7
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,609
    1) Why do you hate 407C? It's just a blended refrigerant - it hasn't done anything to you, has it?
    2) Sounds like you may have heat transfer issues. Probably be a good idea to look at flow first, obstruction next, depending on how the waterside is piped.
    3) Don't want to be the "ugly American", but since this is a U.S. based forum, you might want to convert your temps to F before posting. I, for one, won't go to any great lengths to do that for you, and I know a lot of others that feel the same, so you limit your assistance by using the metric system around here.

  8. #8
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,298
    Quote Originally Posted by klove View Post
    Don't want to be the "ugly American", but since this is a U.S. based forum, you might want to convert your temps to F before posting. I, for one, won't go to any great lengths to do that for you, and I know a lot of others that feel the same, so you limit your assistance by using the metric system around here.

    X2.....

    You will get a lot more responses if you convert to deg F. And you can't convert the delta T, you have to convert the 2 temps to deg F then figure delta T.

  9. #9
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    306
    Quote Originally Posted by R123 View Post
    X2.....

    You will get a lot more responses if you convert to deg F. And you can't convert the delta T, you have to convert the 2 temps to deg F then figure delta T.
    For delta T C to delta T F you can multiply by 1.8 or divide by 1.8 to go from delta F to Delta C. Living in a metric system country and communicating with US factories you get nowhere quick if you cannot be fluent in both languages
    Necessity is the mother of invention

  10. #10
    Join Date
    Nov 2011
    Location
    North sweden, Ume, Where the birches growing without limits.
    Posts
    94
    Repost from original post now with farenheit scales

    Well, i have fighted against a "yurk" chiller (loaded with R407C, yes i hate that refrigerant) that's trippin' on the freeze guard at one circuit, +37f (okay it'ts pure water on the cold side, a +53f/+46f system) Both circuits is a little underfilled, just about to flash in the sight glass.

    However.... Suspicious about flow issues. Both circs is running with almost same values (+37f evap/+104f cond) but the circ thats trippin on freeze guard is running with deltaT 12,5f in/out on the water side, +5,5f subcool, +7f superheat, the other circ is +7,2f sub, +9 superheat and 5c deltaT in/out water side (yup it's plate heat exchangers), my service leader meaned that I would get a lower deltaT on the "problem circ" if I refilled it with refrigerant. But in my book... I would get a higher deltaT if its "Topped up" with missing ref., to get a lower dT, remove some ref. you get less effiency. I know that's its more factors that's making sense. But now. Just focusing on the ref. filling...


    Oh... about my 407C issues... Ok, it might be a good ref. But not for me, i hate refs with big glide. I rather run 134a, 404A (or even better, 507) or 410A, ok 410 uses higer pressures, but that's no problem for me.

  11. #11
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,298
    What kind of York chiller? Air cooled, water cooled, recip, screw, scroll? What's the model number? When you say "freeze guard at one circuit" what do you mean? I would think that would mean low water temp cutout, but that would shut down the whole chiller, not just a circuit. Do you mean "low evap refrigerant temp"?

  12. #12
    Join Date
    Nov 2011
    Location
    North sweden, Ume, Where the birches growing without limits.
    Posts
    94
    water/water, hermetic reciprociating comp, ycwm 150. there's 2 circuits in the chiller, both circs has own plate heat exc's for cold and warm side, the only thing that ties them together is incoming and outgoing water pipes.

    the freeze guard is sensing the liquid (water) temp in the plate exch., tripping the circ that's have too cold liquid temp, if there's flow problem etc.

    ah... the circs is independent of each other...

    got me?

  13. #13
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,267
    flow issues could be the problem. is the safety calibrated and tripping at the setpoint? how are the pressures as it is pulling the load down...stable and steady or losing control and 'wild'? keep in mind that R407c has a very high temperature glide and you must use the appropriate scale for liquid or vapor measurements. i wish we would all go metric...its a lot easier after you get used to it.
    my 1st time jumping out of a plane...http://youtu.be/Kv38G0MHsGo

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event