Results 14 to 26 of 35
-
09-16-2012, 05:57 PM #14
Professional Member
- Join Date
- Aug 2006
- Location
- ohio
- Posts
- 233
-
09-16-2012, 05:59 PM #15
Professional Member
- Join Date
- Aug 2006
- Location
- ohio
- Posts
- 233
ok r123 let me try this. Sorry I was just trying to get some info because I don't have anything on this chiller. thanks in advance.
-
09-16-2012, 06:17 PM #16
Professional Member
- Join Date
- Aug 2006
- Location
- ohio
- Posts
- 233
I will connect with techview in the morning and check and see what the eev position is. Could the extra gallon of oil be enough to coat the tubes in the evaporator and cause the high approach temp? If so will I be able to bring it back running it fully loaded for an hour or will I need to drain it off the bottom of evap? Also is there a tap in tech view that will let me load it manually, it has been awhile?
-
09-16-2012, 07:01 PM #17
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 927
-
09-16-2012, 07:52 PM #18
Professional Member
- Join Date
- Aug 2006
- Location
- ohio
- Posts
- 233
Ok I think I just did. If not please let me know.
-
09-16-2012, 07:58 PM #19
Yes the one extra gallon of oil is screwing the system up .Guess you thought my previous post was just BS . Oil charges on RTACs are critical . You need to run it FULLY UNLOADED to recover the oil . Running unloaded raises your DSH and increases oil separation . Correct your oil level then you can worry about EXV position etc . Until your oil level is correct your p$$#%%G in the wind
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
09-16-2012, 08:39 PM #20
I can't count how many RTAC's I have come to where company X has somehow added and extra gallon or 2 of oil. There is even a service bulletin out about some factory shipped units with to much oil.
I just have to ask if you pulled 3 gals out and nameplate states 2, why, why would you put 3 back in? why?.It's hard to stop a Trane. but I have made one helluva living keeping them going.
-
09-16-2012, 09:19 PM #21
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 927
-
09-16-2012, 09:45 PM #22
Did you weigh in nameplate refrigerant charge?
-
09-16-2012, 09:46 PM #23
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,550
-
09-16-2012, 10:00 PM #24
Professional Member
- Join Date
- Aug 2006
- Location
- ohio
- Posts
- 233
I looked everywhere and cant find private messenger. My email is there.
-
09-16-2012, 10:08 PM #25
Professional Member
- Join Date
- Aug 2006
- Location
- ohio
- Posts
- 233
No I didn't think it was bs, I am used to the old rtaas that have a larger oil separators and over on oil wasn't a big deal. I just figured since it had that much in it from the factory for this long is wasn't a big deal. But maybe that had something to do with the compressor failing? Any info I get here is appreciated. Is there a tab to manually load in techview or will I have to jump out the load relay and un-wire the unload relay?
-
09-16-2012, 10:19 PM #26
Professional Member
- Join Date
- Feb 2012
- Location
- EVERYWHERE
- Posts
- 164
Just remove the extra oil your added over the nameplate. To much oil can kill the compressor.



Reply With Quote