  1. #27
    I am in reading pa can i call you?

  2. #28
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,826
    You said it's pumping down but failed to say what the low pressure control is set at.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  3. #29
    is that why just the top of the evaporator is frosting?

  4. #30
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    If jp had a dollar for every time he's linked that sporlan headmaster charging document.....you'd be able to retire!

    On a more serious note, sounds like its time for you to put your cold weather gear on and take some superheat readings after topping the charge off....

  5. #31
    you are right!!!! jp is pretty smart good guy to have on our side

  6. #32
    that is probably why only the top of evap has a frost pattern

  7. #33
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    I've learned probably more from him than any of the guys I work with, honestly. 2sac, icemeister, phase loss, and cracker too just to an,e a few more who are awesome.

  8. #34
    so tell me undercharged system would cause frost pattern only on the top of evap right

  9. #35
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,916
    Thanks, guys. You're making me blush.

    gcmechanical,

    I'll answer any question that you've got here on the forums.


    Yes, low charge will cause uneven frost patterns as well.

  10. #36
    jp i really thank you i appriciate your expertise and feel confident that this is the issue good night

  11. #37
    i will send you the out come friday

  12. #38
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,916
    Quote Originally Posted by gcmechanical View Post
    i will send you the out come friday

    Thanks.

    Now, 2sac makes a good point, too.

    Take a few extra minutes and verify the settings of all of the operating controls.

    http://www.heatcraftrpd.com/products...%5CH-IM-CU.pdf

    There's another good document for ya.

  13. #39
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,596
    I took that to mean that it was shutting down on low pressure jp.

    2sac always makes good points, how could you go wrong with a guy who has Al Bundy as an avatar??? That makes me laugh every time I see it.

Page 3 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event