    A good lesson you've learned here is to never trust a sticker.
    Always trust your knowledge and tools over a sticker.
  2. #41
    Oct 2011
    Chicagoland Area
    Quote Originally Posted by ryan1088 View Post
    I took that to mean that it was shutting down on low pressure jp.
    2sac always makes good points, how could you go wrong with a guy who has Al Bundy as an avatar??? That makes me laugh every time I see it.
    I have never claimed to know anything about anything, but thank you for the compliment.
    As far as Al Bundy is concerned
    Local 597 Service Fitter
    Metal Trade Journeyman
    PAY ME NOW OR PAY ME LATER
    It was working when I left...
    WWFD
  3. #42
    When you get to a system that is operating sporadically, take your time. Step back, and look at the big picture. Pressure control settings, superheat, subcooling, coil cleanliness, etc. . Review all of the basics, and assume that the last guy that worked on it was wrong and messed things up. Chances are, you will be right. Look at the big picture, and narrow it down from there.
  4. #43
    Does the unit have a Low Pressure Control Bypass Timer?
  5. #44
    Sounds like it's undercharged