Results 40 to 44 of 44
Thread: system pumping down low ambient
-
09-13-2012, 03:18 PM #40
A good lesson you've learned here is to never trust a sticker.
Always trust your knowledge and tools over a sticker.
-
09-13-2012, 03:46 PM #41
-
09-19-2012, 12:00 AM #42
Regular Guest
- Join Date
- Sep 2012
- Posts
- 15
When you get to a system that is operating sporadically, take your time. Step back, and look at the big picture. Pressure control settings, superheat, subcooling, coil cleanliness, etc. . Review all of the basics, and assume that the last guy that worked on it was wrong and messed things up. Chances are, you will be right. Look at the big picture, and narrow it down from there.
-
09-19-2012, 12:07 AM #43
Regular Guest
- Join Date
- Sep 2012
- Posts
- 15
Does the unit have a Low Pressure Control Bypass Timer?
-
09-19-2012, 03:51 PM #44
Professional Member
- Join Date
- Dec 2004
- Posts
- 484
Sounds like it's undercharged


Reply With Quote