system pumping down low ambient
Hi out there, I have a walk in freezer prior company kept charging system 2 times a year without finding leak. I got called out pumped system up with inhert gas found leak fixed it and installed new drier. two days later got called out unit not cooling sight glass yellow. pumed system down installed another new drier and evacuated system for 5 hours, system worked well for 2 weeks. got called out today sight glass green full of charge system works during the day but at night when temp goes down to 50 degrees unit pumps down. turn system off for 20 min and turn it back on system runs normally can anyone advise
-
09-12-2012, 08:30 PM #2
Moved to Refrigeration and Ice Making Forum
-
09-12-2012, 08:32 PM #3
Ok, gotta pick this apart, piece by piece...
Do you have a micron gauge? Did you use it?evacuated system for 5 hours
Is this an outdoor unit? Does the unit have a headmaster control?sight glass green full of charge system works during the day but at night when temp goes down to 50 degrees unit pumps down.
-
09-12-2012, 08:38 PM #4
Regular Guest
- Join Date
- Sep 2012
- Posts
- 20
yes condenser is on the roof of building and it does have a head master i thought that it was non condensables due to prior refrigeration company charging without fixing leak was on the low side vibration eliminator i fix it and change drier 3 times and evacuated 5 hours on last attempt now sight glass is green and system runs fine during that day but at night it fails. when i arrive in the mornind it is short cycling
-
09-12-2012, 08:39 PM #5
Regular Guest
- Join Date
- Sep 2012
- Posts
- 20
and yes 300 microns
-
09-12-2012, 08:42 PM #6
-
09-12-2012, 08:43 PM #7
When you get there in the morning, what is the condition of the glass?
What are the operating pressures?
-
09-12-2012, 08:43 PM #8
Regular Guest
- Join Date
- Sep 2012
- Posts
- 20
also forgot to mention when i took drier off for the first time the bottom line was full of oil could the system be oil bound
-
09-12-2012, 08:46 PM #9
Regular Guest
- Join Date
- Sep 2012
- Posts
- 20
thought it was non condensables before 300 microns. 404a refrigerant head pressure 200 suction starts at 50 psi and falles until low pressure cut out.
-
09-12-2012, 08:47 PM #10
Regular Guest
- Join Date
- Sep 2012
- Posts
- 20
new txv and now i think the system may be oil bound suction line is frosting but not all the way back to compressor
-
09-12-2012, 08:51 PM #11
Did you charge the system properly for headmaster operation?
-
09-12-2012, 08:52 PM #12
-
09-12-2012, 08:53 PM #13
Regular Guest
- Join Date
- Sep 2012
- Posts
- 20
you lost me i weighed in charge and cleared sight glass how do you charge for head master operation i did not know there was a differance for that tell me how


Reply With Quote