Thread: Being told I need to replace entire system because coil in air handler is bad

  1. #1
    Join Date
    Sep 2012
    Posts
    4
    Post Likes

    Being told I need to replace entire system because coil in air handler is bad

    Hello, my family just moved into a new house a few months ago. We were told that the A.C. was new-ish when we purchased the home. Well, we noticed that the central A.C. would freeze up every 2-3 weeks. We'd clean the filter, thaw it out and it would run again for another 3 week period and freeze up again.

    So we called a repairman out to take a look. He told us that the previous owners had only replaced the big outside unit which contains the compressor and that the outside unit looks to be installed a few years ago and was manufactured in 2003.

    But he said they didn't replace the inside unit which was built in 1996 and has rusted coils and is totally filthy/gunked up. Repairman suggested that we buy a new inside unit since outside unit is relatively new and skip replacing coils.

    But he couldn't give us an estimate as what anything would cost.

    His boss called me today to give me a quote and said that the coil in my air handler is bad. He said that I could either replace the air handler and modify it to work with the old kind of refrigerant my unit takes - or - replace both the inside and outside units. He said that replacing the air handler is a bad idea because it has to be modified to fit old refrigerant and if either the outside or inside unit breaks the costs to repair would be astronomical due to this refrigerant issue.

    Seems like it shouldn't be such a big deal to just replace the rusted coils and clean the Unit but he definitely did not agree with that plan of action. He also insisted that I replace the outside component as well, not just the inside, which dismayed me because I was under impression it was relatively new.

    Am I crazy for thinking that there's a simpler solution other than replacing everything inside AND outside?

    Hope that made sense, thanks!

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by mgs9988 View Post
    Hello, my family just moved into a new house a few months ago. We were told that the A.C. was new-ish when we purchased the home. Well, we noticed that the central A.C. would freeze up every 2-3 weeks. We'd clean the filter, thaw it out and it would run again for another 3 week period and freeze up again.

    So we called a repairman out to take a look. He told us that the previous owners had only replaced the big outside unit which contains the compressor and that the outside unit looks to be installed a few years ago and was manufactured in 2003.

    But he said they didn't replace the inside unit which was built in 1996 and has rusted coils and is totally filthy/gunked up. Repairman suggested that we buy a new inside unit since outside unit is relatively new and skip replacing coils.

    But he couldn't give us an estimate as what anything would cost.

    His boss called me today to give me a quote and said that the coil in my air handler is bad. He said that I could either replace the air handler and modify it to work with the old kind of refrigerant my unit takes - or - replace both the inside and outside units. He said that replacing the air handler is a bad idea because it has to be modified to fit old refrigerant and if either the outside or inside unit breaks the costs to repair would be astronomical due to this refrigerant issue.

    Seems like it shouldn't be such a big deal to just replace the rusted coils and clean the Unit but he definitely did not agree with that plan of action. He also insisted that I replace the outside component as well, not just the inside, which dismayed me because I was under impression it was relatively new.

    Am I crazy for thinking that there's a simpler solution other than replacing everything inside AND outside?

    Hope that made sense, thanks!
    Post the model and serial number of indoor and out will help. Labels are on the equipment

  3. #3
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    I understand your frustration. It should be simple but unfortunately it is not. EPA regulations and energy efficiency requirements, which seem to change yearly now, have muddied the water. There are to many to try to cover here but what you may be facing is you have an R22 system with a SEER rating that is no longer produced due to the before mentioned regulations. And in order to replace one piece of your system you may indeed need to replace all of it. There are, as far as I know still some "dry units" available from some manufacturers that may be applicable to your situation. However since R22 is being phased out, EPA regulation agin, it's cost will indeed sky rocket. I recommend having a second company evaluate and give you options and compare, always a good idea, and ask questions. A good tech or manager will take the time to explain your issue so that you understand the why. Oh ya then call your congressman and ask him too.

  4. #4
    Join Date
    Sep 2012
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by second opinion View Post
    Post the model and serial number of indoor and out will help. Labels are on the equipment
    here's what I could find thanks:

    Inside unit:

    Top/Upper Half :

    Rheem / M# RCGA 48A1A521 / S# M1096

    Lower Half:

    Rheem / M# REBA21J10NUEAI / S# T M1096 05038

    Outside Unit:

    Rheem

    M# RAND 048JAZ

    S# 7303 M2406 19892

  5. #5
    Join Date
    Jul 2009
    Location
    King Ranch Texas
    Posts
    216
    Post Likes
    so no one has diagnosed a leak, so lack of airflow from a dirty coil is one option causing your issue. I would have the coil pulled and cleaned before replacing it if there has not been an actual diagnosis of a leaking coil. When you look at the coil does it appear dirty or clogged enough to restrict airflow?
    Sic semper tyrannis

    ‚——’ฏฏ‘;====ฑ—- * * * * * *
    !‚–’ฏฏƒนถ

  6. #6
    Join Date
    Sep 2012
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by Integrity Aire View Post
    so no one has diagnosed a leak, so lack of airflow from a dirty coil is one option causing your issue. I would have the coil pulled and cleaned before replacing it if there has not been an actual diagnosis of a leaking coil. When you look at the coil does it appear dirty or clogged enough to restrict airflow?
    not sure. The repairman that came out did not say anything was wrong with anything that was in the Outside unit. the coils inside the Inside unit were freezing up. The coils themselves don't look dirty but there is certainly a ton of gunk up in the inside unit.

    Repairman said that the coils in the inside of the unit are rusted.

    but they're not rusted through and there was no diagnosis of leakage. the issue that he seemed MOST concerned about was the dirtiness of the Unit.

  7. #7
    Join Date
    Jul 2012
    Location
    Western KY
    Posts
    1,221
    Post Likes
    Quote Originally Posted by mgs9988 View Post
    not sure. The repairman that came out did not say anything was wrong with anything that was in the Outside unit. the coils inside the Inside unit were freezing up. The coils themselves don't look dirty but there is certainly a ton of gunk up in the inside unit.

    Repairman said that the coils in the inside of the unit are rusted.

    but they're not rusted through and there was no diagnosis of leakage. the issue that he seemed MOST concerned about was the dirtiness of the Unit.
    I missunderstood your problem. If there was no leak diagnosed and only a dirty coil issue stated as reason to replace call them back and ask why the coil was not cleaned first of all. Then bite the bullet and call a reputable service company to come service the system properly before any thought of replacing. As I said earlier replacing may require whole system and will be very expensive. If its just dirty it should have been cleaned not condemned.

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I'd get another company in to clean the indoor coil. Since you don't say that any refrigerant had to be added any of the times it froze up.

  9. #9
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    with somewhat vague info relayed, a second opinion would definitely be in order.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  10. #10
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Rheem coils are just impossible to clean without removing it.

    If it ain't pulled (coil and fan) than it ain't clean. IMHO.

  11. #11
    Join Date
    Feb 2004
    Location
    michigan
    Posts
    677
    Post Likes
    Quote Originally Posted by SBKold View Post
    Rheem coils are just impossible to clean without removing it.

    If it ain't pulled (coil and fan) than it ain't clean. IMHO.
    Right on!
    I am the "Wally". All others are meer imitations of the original.

  12. #12
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    First optioin I would try cleaning the coil. Second option repalce the air handler with a new Trane. They have a couple models that change for different refrigerants with a switch. So if you need to change the outdoor unit in the future all that needs to be done is fllip the switch and flush the coil to remove residual oil, etc. It saves the hassle of changing TXV's the having ot change it back later if refrigerants are changed.

  13. #13
    Join Date
    Aug 2012
    Posts
    3,771
    Post Likes
    Quote Originally Posted by kls-ccc View Post
    First optioin I would try cleaning the coil. Second option repalce the air handler with a new Trane. They have a couple models that change for different refrigerants with a switch. So if you need to change the outdoor unit in the future all that needs to be done is fllip the switch and flush the coil to remove residual oil, etc. It saves the hassle of changing TXV's the having ot change it back later if refrigerants are changed.
    what is the model num. of that unit please.

  14. #14
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    As I understand TAM4, TAM7, and TAM8

  15. #15
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by mgs9988 View Post
    Hello, my family just moved into a new house a few months ago. We were told that the A.C. was new-ish when we purchased the home. Well, we noticed that the central A.C. would freeze up every 2-3 weeks. We'd clean the filter, thaw it out and it would run again for another 3 week period and freeze up again.

    So we called a repairman out to take a look. He told us that the previous owners had only replaced the big outside unit which contains the compressor and that the outside unit looks to be installed a few years ago and was manufactured in 2003.

    But he said they didn't replace the inside unit which was built in 1996 and has rusted coils and is totally filthy/gunked up. Repairman suggested that we buy a new inside unit since outside unit is relatively new and skip replacing coils.

    But he couldn't give us an estimate as what anything would cost.

    His boss called me today to give me a quote and said that the coil in my air handler is bad. He said that I could either replace the air handler and modify it to work with the old kind of refrigerant my unit takes - or - replace both the inside and outside units. He said that replacing the air handler is a bad idea because it has to be modified to fit old refrigerant and if either the outside or inside unit breaks the costs to repair would be astronomical due to this refrigerant issue.

    Seems like it shouldn't be such a big deal to just replace the rusted coils and clean the Unit but he definitely did not agree with that plan of action. He also insisted that I replace the outside component as well, not just the inside, which dismayed me because I was under impression it was relatively new.

    Am I crazy for thinking that there's a simpler solution other than replacing everything inside AND outside?

    Hope that made sense, thanks!
    There are other reasons that freeze coils. Not enough air flow can be caused by a dirty blower, a low fan setting, and restricted ducts. Check the blower for dirt. Open all of the supply grills in the home. Check the blower for a high speed setting.
    The last cause is the setting of the t-stat. Raise your setting of the t-stat a couple degrees during cool outside temps to avoid below freezing coil temps. Fan "on" mode also will quickly defrost a coil that is partially frozen.
    Wide dead band t-Stat will freeze up sooner than narrow band stats.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  16. #16
    Join Date
    Sep 2012
    Posts
    4
    Post Likes
    Thread Starter
    Thank you for all the great input.

    Based upon what I read here, I asked another company to come out and take a look to get a fresh perspective.

    They more or less concurred that both units need to be replaced. The coolant in the outside unit WAS low, apparently about 3/4 of the way gone. Although they didn't say that the outside unit had any problems re: coil, they concurred that the coil in the Inside unit was rusted and needed to be replaced.

    They said they wouldn't recommend cleaning the coil because of the age of the Unit (1996) because cleaning it could damage it.

    So it's looking like I need to replace the whole system and will look for the most affordable option. I think calling out a third company is overkill.

  17. #17
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    Are you using pleated 1" wide air filters? The reason I ask is because these highly restrictive air filters will CAUSE the indoor unit to freeze up within just a couple of weeks!! Go to the less restrictive throw away filters and quit using the pleated (zig zag type) filters!!

  18. #18
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    If it can be budgeted i would replace it all ,i also beleive that the evaporator is still made for the unit and could be replaced .

  19. #19
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    Quote Originally Posted by mgs9988 View Post
    Thank you for all the great input.

    Based upon what I read here, I asked another company to come out and take a look to get a fresh perspective.

    They more or less concurred that both units need to be replaced. The coolant in the outside unit WAS low, apparently about 3/4 of the way gone. Although they didn't say that the outside unit had any problems re: coil, they concurred that the coil in the Inside unit was rusted and needed to be replaced.

    They said they wouldn't recommend cleaning the coil because of the age of the Unit (1996) because cleaning it could damage it.

    So it's looking like I need to replace the whole system and will look for the most affordable option. I think calling out a third company is overkill.
    For some reason my BS flag started waving. If the unit was low on Refrigerant it would cause freeze ups, but if it was 3/4 low it would not cool. Also if it was that low the first guy should have caught it, most guys love to throw refrigerant at stuff and proclaim it fixed.

    Don't misunderstand I am not saying that you shouldn't replace the inside unit but I don't think you are getting the complete story on the condition of your equipment or what the actual problem is. AS I and others have said you need to have the airflow checked first, then once that is correct start to look further into the problem if it is not fixed.

    It is hard to make a good decision with bad info.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •