What application is the TEC using? Check the application point list. If you can change the action there will be a binary point to change the action. You should then be able to change the action from the Insight. You will need to back up the TEC to the panel and the panel to the Insight to make sure the changes are backed up and won't be reversed if the TEC loses power, this will cause a reload of the TEC point list in the panel.